Vaulted Ceiling vs BTU

I found this sticky thread in this forum: http://www.doityourself.com/forum/ai...ing-chart.html


Is this list for standard height walls (9-10 feet in height)?

I am curious. If I have a room that is about 300 sq feet and also has a vaulted ceiling (an additional 9 feet in height with a 45 slant), do I add another 150 sq feet and get a 12K BTU instead of a 8K BTU?

Forum Moderator: I apologize that I posted this in the wrong forum. I was reading between threads and accidentally posted here. Can you move this to the AC forum? Thanks
 
Sponsored Links
  #2  
Old 06-17-16, 03:48 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
Standard ceiling height is eight feet. That chart is a VERY rough rule of thumb and cannot be relied upon for anything more than a rough idea. You could run a quick and dirty heat gain calculation on the single room and probably get a better answer. Here's one that takes into account the total volume of the room. Warmair.com - Window Air Conditioners Figure the height as 1/2 the difference between the top of the walls and the top of the peak plus the height of the walls.

Example: Walls are ten feet high and the peak is nineteen feet high. Divide the extra nine feet by two and 4-1/2 feet. Add this to the ten feet of the walls for a calculated height of 14-1/2 feet.

Do NOT oversize the unit. Much of the comfort in air conditioning comes from the reduction in the relative humidity (RH) in the room. An oversized A/C will quickly chill the room and then shut off under control of the thermostat. That leaves you with an even higher RH plus cold temperatures, a miserable condition. Ideally the A/C should run continuously on the hottest days.
 
  #3  
Old 06-17-16, 12:23 PM
WRDIY's Avatar
Member
Thread Starter
Join Date: Jul 2012
Posts: 678
Received 4 Votes on 3 Posts
Furd, thanks for providing the insights and knowledge.

Originally Posted by Furd
Do NOT oversize the unit. Much of the comfort in air conditioning comes from the reduction in the relative humidity (RH) in the room. An oversized A/C will quickly chill the room and then shut off under control of the thermostat. That leaves you with an even higher RH plus cold temperatures, a miserable condition. Ideally the A/C should run continuously on the hottest days.
I never knew that. I always thought that "oversized" is better. Very good knowledge to know.

The AC Window Unit that I have can continue to run without shutting off. It has a continuous mode. If I "OverSize", would that matter?

Thanks Furd.
 
  #4  
Old 06-17-16, 01:21 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
The continuous mode merely keeps the fan running while the compressor cycles with the thermostat. Leaving the fan running while the compressor is off will cause the moisture that has condensed on the evaporator (cooling) coil to re-evaporate into the room air and that will raise the RH. There are very few instances when continuous fan operation of an air conditioner is beneficial.
 
  #5  
Old 06-17-16, 01:37 PM
WRDIY's Avatar
Member
Thread Starter
Join Date: Jul 2012
Posts: 678
Received 4 Votes on 3 Posts
Thanks for the follow up Furd.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: