3 year old AC not cooling


  #1  
Old 07-01-19, 06:54 PM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
3 year old AC not cooling

Hello all,
i live on the east coast of Florida home was built in 2001 1890SQFt Trane AC was replaced 3 years ago. all summer the AC has been running non stop and won’t get below 80-83 during the day. AC company came out 2 weeks ago and installed 2 lbs of Freon. No change in temperature. Came back
1 week ago and found very tiny pine hole leak on coil inside garage. Said I was still full on Freon but unit isn’t cooling return temperature is 73. Vents are 58-62. The coil is under warranty. I will just be paying for labor and they can possibly reuse the Freon. But I don’t believe this will solve my issue. My electric bill has been $280-300. Should be around 150-180. Any help would be greatly appreciated.
-thanks Brian
 
emille085 voted this post useful.
  #2  
Old 07-01-19, 07:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,937
Received 3,951 Upvotes on 3,544 Posts
Welcome to the forums.

It's been installed for three years.
Was it working perfectly year one and two ?
 
  #3  
Old 07-02-19, 02:37 AM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
You know how that Florida heat is. It worked and would keep the house around 77-78. I believe it’s a 3.5 ton unit. The AC guy said it’s plenty of power for this size house.
 
  #4  
Old 07-02-19, 05:52 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Hi, you are getting approximately 10* drop across the coil, that might be a little low, let’s see what the HVAC pro’s say.
Geo
 
  #5  
Old 07-02-19, 07:38 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,657
Received 2,153 Upvotes on 1,928 Posts
How can your return temperature be 73f when your house is 83 ?

Go around your house and feel every vent when the system is running. Is air blowing out of all of them about equally? Just checking to make sure you haven't had a duct come loose or get pinched closed. It also wouldn't hurt the check the return ducting.

Have you replaced your air filter?
 
  #6  
Old 07-02-19, 09:11 AM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
The return is About 5 inches from the floor. Thermostat is eye level. It’s reading 73-75 at the return. 80’s at eye level and 85-87 In the corners up high. We have y’all ceiling.
Move checked all the vents they all range from 58-62. 10 total vents with a average temp of 60. AC filter gets changed ever other month. Coil looks clean, except for the oil/Freon leak.
 
  #7  
Old 07-02-19, 10:09 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,657
Received 2,153 Upvotes on 1,928 Posts
What is "y'all" ceiling??? Do you mean a vaulted or cathedral ceiling?

Are your registers located in the floor? 12-15 degree difference between the floor and ceiling isn't good. It might be acceptable in the peak of a vaulted ceiling but with normal flat ceilings that seems excessive and uncomfortable. My head would be sweating while my feet are cold.
 
  #8  
Old 07-02-19, 02:28 PM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
Tall ceilings haha. Vaulted ceiling. They just quoted me $330 to replace the coil that is under warranty. And reuse the Freon
 
  #9  
Old 07-02-19, 07:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,937
Received 3,951 Upvotes on 3,544 Posts
Sounds like a good deal to me.

Did they say what the problem was with the old one ?
 
  #10  
Old 07-02-19, 08:48 PM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
I don’t for see this fixing the issue. 2 weeks ago they added 2lbs of Freon. Did not notice any change in temperature or how much the system ran. They came back out a week later and found pin hole leak in coil. System was still fully charged.
If the system is fully charged but I have a pin hole leak everything should be working properly and cooling the house.
I could understand if I was low on Freon and the house was hot. But I’m full and house is 80-83 degrees
 
  #11  
Old 07-03-19, 03:55 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Hi, did this system ever cool the house?
Geo
 
  #12  
Old 07-03-19, 05:44 AM
B
Member
Thread Starter
Join Date: Jul 2019
Posts: 6
Upvotes: 0
Received 1 Upvote on 1 Post
No. He recharged the system. Coil still has a small leak but is currently full after 2 weeks. Debating weather or not to spend 350 on the new coil.
 
 