Tankless / Steam Operation


  #1  
Old 03-07-18, 06:07 AM
S
Member
Thread Starter
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tankless / Steam Operation

I understand on hot water / tankless, the aquastat tells the burner to come on when hot water is needed, and if there is no call for heat, the circulators are off and no heat is delivered to the house. But how does this work with steam, since there are no valves or pumps? When tankless calls for heat, eventually won't you always get some heat thru the radiators? Or does the boiler shut off before the water can get hot enough to produce steam?
 
  #2  
Old 03-07-18, 08:42 AM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,768
Received 141 Upvotes on 133 Posts
S,
There is a separate aquastat for domestic hot water installed on your boiler.

During the off season and when there is no call for heat if the temp in the boiler drops to what the aquastat is set for, usually around 180, since that is the temp the coil is designed for to produce sufficient hot water, the boiler will come on and maintain that temp like a regular hot water boiler.

Since steam is made at 212 the boiler never gets hot enough to send steam to the rads.

Hope this helps a little.
 
 