Bad tankless coil cause overheating?


  #1  
Old 10-07-18, 08:33 AM
S
Member
Thread Starter
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
Bad tankless coil cause overheating?

Oil boiler is 16 yrs old with orginal coil. Hot water has been lacking for a couple years now, I assume poor heat transfer. Flushed the coil with that solution last year and got a slight improvement. Sometimes over the past year, the boiler would overheat to 230 and the baseboard had popping sounds, probably steam. I replaced the aquastat thinking the high limit switch was bad and the problem remained. Could an old, tankless coil with bad heat transfer cause the boiler to overheat? I'm not sure what else could cause this.

Thanks.
 
  #2  
Old 10-07-18, 10:47 AM
G
Member
Join Date: Nov 2011
Location: USA
Posts: 593
Upvotes: 0
Received 2 Upvotes on 2 Posts
Once in a blue moon I had to use something like this to get hot water from a standing coil.Maybe your aquastat well is scaled on the outside. Good luck.https://www.comstarproducts.com/boil-a-coil-16-ounce-12
 
  #3  
Old 10-07-18, 10:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,921
Received 3,758 Upvotes on 3,369 Posts
It sounds like the aquastat is not registering the actual water temperature. That could be from corrosion built up on the well inside the boiler. The tankless coil will not cause the boiler to overheat.
 
  #4  
Old 10-07-18, 10:58 AM
S
Member
Thread Starter
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
If you say the aquastat probe well can make it overheat, then wouldn't that mean the coil in effect is making it overheat, since they are all one piece? Sounds like only remedy is to replace the coil.
 
  #5  
Old 10-07-18, 11:06 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,921
Received 3,758 Upvotes on 3,369 Posts
The boiler is a tank of water. The well sits in that hot water as well as the tankless coil. As DHW is used.... cold water enters the coil and it will always be cooler than the tank temperature.

The aquastat monitors the boiler water temperature. It doesn't care if there is a tankless coil there or not.
 
  #6  
Old 10-07-18, 05:52 PM
S
Member
Thread Starter
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
I get that, but in this case it is in the coil, so to fix a probe well issue, don't you have to replace the coil?
 
  #7  
Old 10-07-18, 06:06 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,754
Received 137 Upvotes on 129 Posts
No you don't. The well just unscrews from the coil plate. You must drain the boiler below the location of the well because when you remove it the boiler water will drain from the open hole.

http://www.supplyhouse.com/Honeywell...Well-3712000-p

They also come in 3/4" which you can find on the same sight.

Hope this helps a little.
 
  #8  
Old 10-11-18, 08:18 AM
S
Member
Thread Starter
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
Replaced the coil last night. I see what you mean about the threaded well. The probe well looked pretty clean, but the boiler doesn't overheat anymore, so I'm not sure how a new coil fixed that. But the hot water is awesome now.
 
Attached Images         
  #9  
Old 11-12-18, 05:28 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,454
Upvotes: 0
Received 267 Upvotes on 243 Posts
If flushing the coil only improved the hot water a little and replacing the coil improved it a lot then the coil still had a lot of lime or other sediment inside.

The probe attached to the coil mounting plate was probably malfunctioning, continuing to call for heat long after the boiler went above its usual temperature.
 
 