i have a bunch of posts cant find them? i replaced chamber unit relief valve and pressure gauge furnace has been working fine.i noticed gauge goes up to 30 psi.seem high. this is a 1986 dunkirk steam furnace thanks for any help
 
  #2  
Old 02-18-19, 12:24 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 3,378
Received 119 Likes on 113 Posts
b,
Found your old posts. Your relief valve should go off at 15 PSI. As previously mentioned you do not need any more than 2 PSI in to run your boiler. Your boiler is a 1984 Dunkirk as stated in an older post.

Pics would be helpful if possible to see the equipment.
 

Last edited by spott; 02-18-19 at 01:24 PM.
  #3  
Old 02-18-19, 12:40 PM
Shadeladie's Avatar
Super Moderator
Join Date: Jan 2005
Location: PA - USA
Posts: 5,036
Received 321 Likes on 255 Posts
Just click on your name and pick "find all posts" to find your previous posts.

I think this is the thread you're looking for:

Fire brick?
 
  #4  
Old 02-18-19, 06:03 PM
B
Member
Thread Starter
Join Date: Feb 2012
Location: usa
Posts: 18
Likes: 0
Received 0 Likes on 0 Posts
what makes the pressure go so high?
 
  #5  
Old 02-18-19, 06:29 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 3,378
Received 119 Likes on 113 Posts
Is your relief valve going off. If not, either your gauge is defective or your relief valve is defective. Your pressuretrol settings controls your high limit.
 
  #6  
Old 02-20-19, 03:58 AM
S
Member
Join Date: Jan 2017
Location: USA
Posts: 568
Likes: 0
Received 13 Likes on 10 Posts
If your boiler is a steam boiler and the steam pressure is actually raising to 30 psi with a 15 steam safety valve, which is the correct pressure rating for a steam boiler, it is time to have someone fix this problem immediately and I mean right now, before this boiler hurts you or your family. This is what we call a "run away boiler" and it is very dangerous.
 
 