hot water boiler

i got a now burnham oil boiler installed they put the circulator pump on the return line with the arrow pointed toward the boiler they put the expansion tank on the the supply pipe will this work
 
Sponsored Links
  #2  
Old 11-04-19, 11:34 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
Probably, but it is wrong. The pump should ALWAYS pump away from the expansion tank connection.
If the pump is on the boiler return piping then the expansion tank should be connected on the return piping before the pump. Since this raises other concerns it is best to simply mount the pump on the supply piping after the air elimination device.
 
  #3  
Old 11-05-19, 12:25 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 837
Received 23 Votes on 22 Posts
Yes it will work and in most systems it does not make noticeable difference.

Theory is one thing, actual practice another.

If the system heats the place satisfactorily without issues, just live with thought of imperfect design.

Mine are mounted upside down on floor and connected to return line / boiler input. When a diaphragm goes does not have to wrestle with heavy water filled tank or worry about stress on hydronic lines.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: