Combi Boiler


  #1  
Old 01-04-23, 04:01 PM
T
Member
Thread Starter
Join Date: Jan 2023
Posts: 2
Received 0 Upvotes on 0 Posts
Combi Boiler

I recently installed a Bosch Greenstar Combi 100p. I'm using it only to heat cast iron radiators, not for DHW. I hooked up my house thermostat to a Taco SR501-4 Switching Relay. The problem is that every time the thermostat calls for heat, the boiler throws a communication fault A8. Any suggestions would be appreaciated.
 
  #2  
Old 01-04-23, 05:02 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,404
Upvotes: 0
Received 64 Upvotes on 54 Posts
This is looking for a multiple boiler operation. Check the manual and see how to change to a single boiler application.

 
trock121 voted this post useful.
  #3  
Old 01-10-23, 05:02 PM
T
Member
Thread Starter
Join Date: Jan 2023
Posts: 2
Received 0 Upvotes on 0 Posts
You were right. I double checked the Appliance Type 4e setting and it was no longer Central Heating Only, but had reverted to Combi Mode. I reprogrammed it and watched it save the value, but every time I exit Service Mode it reverts to Combi Mode. There must be something I have to change first to allow Operation in Central Heating. I suspect disabling something in DHW, but can't find anything promising. Do you have any suggestions?
 
 