Combi Boiler
#1
Member
Thread Starter
Combi Boiler
I recently installed a Bosch Greenstar Combi 100p. I'm using it only to heat cast iron radiators, not for DHW. I hooked up my house thermostat to a Taco SR501-4 Switching Relay. The problem is that every time the thermostat calls for heat, the boiler throws a communication fault A8. Any suggestions would be appreaciated.
#2
This is looking for a multiple boiler operation. Check the manual and see how to change to a single boiler application.
trock121
voted this post useful.
#3
Member
Thread Starter
You were right. I double checked the Appliance Type 4e setting and it was no longer Central Heating Only, but had reverted to Combi Mode. I reprogrammed it and watched it save the value, but every time I exit Service Mode it reverts to Combi Mode. There must be something I have to change first to allow Operation in Central Heating. I suspect disabling something in DHW, but can't find anything promising. Do you have any suggestions?