Conduit System Components - Help!


  #1  
Old 02-22-16, 09:54 PM
D
Member
Thread Starter
Join Date: Sep 2014
Posts: 31
Upvotes: 0
Received 0 Upvotes on 0 Posts
Conduit System Components - Help!

I have a weatherproof electrical box that I want to mount on a fence. And I have a weatherproof electrical box that I want to mount on a post about 6 feet away. I have a trench dug between them already that is about 18 inches deep and the earth is soft and easy to dig.

The electrical boxes have 3/4 pipe thread. I have 3/4 PVC conduit for the underground portion. How do I connect the conduit coming up from the ground to the two electrical boxes? Since they have threads, something needs to turn, and the boxes can't since they are blocked by their mounting surfaces. I haven't seen fittings that are pipe thread on one end and PVC compression on the other. So I think I need to put the threaded components into each electrical box, then glue the two halves of the system together at a point that is away from the electrical box. Is that the process or am I missing something? This of course can never be disassembled. A list of components, starting at one electrical box, would be appreciated.
 
  #2  
Old 02-22-16, 10:23 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,074
Received 3,600 Upvotes on 3,228 Posts
You would screw 3/4" PVC connectors into the box(es) first. Then the pipe would be glued into the fittings. No need to have to turn the box(es).

Name:  pvc.jpg
Views: 203
Size:  3.9 KB
 
  #3  
Old 02-22-16, 11:42 PM
L
Member
Join Date: Nov 2015
Posts: 1,557
Received 195 Upvotes on 167 Posts
In addition to PJmax's answer, put some sort of thread sealant (same ones you use for plumbing) for additional water proofing. Both caps and male adapters.
I found rain water sometimes leaks in from the thread.
 
  #4  
Old 02-23-16, 06:02 AM
D
Member
Thread Starter
Join Date: Sep 2014
Posts: 31
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks.

How do I connect 3/4 EMT to the 3/4 pipe thread on the weathertight box?
 
  #5  
Old 02-23-16, 06:25 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
How do I connect 3/4 EMT to the 3/4 pipe thread
Use a rain-tight threaded adapter.

Name:  emt.jpg
Views: 188
Size:  25.3 KB .
 
  #6  
Old 02-23-16, 09:06 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,074
Received 3,600 Upvotes on 3,228 Posts
If the fittings are screwed into the bottom of the box then no sealant is required. It's actually better to allow any lost water to be able to find it's way out.
 
  #7  
Old 02-23-16, 10:15 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,014
Received 158 Upvotes on 144 Posts
Are you using EMT or PVC??????????
 
  #8  
Old 02-23-16, 02:25 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,920
Received 175 Upvotes on 153 Posts
EMT is not for burial. It would rust out in a few years.
 
  #9  
Old 02-23-16, 02:47 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I read it as EMT along the fence then PVC to the receptacle on the post.
 
  #10  
Old 02-24-16, 04:06 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
I have a weatherproof electrical box that I want to mount on a post about 6 feet away. I have a trench dug between them already that is about 18 inches deep and the earth is soft and easy to dig.
I read it to mean the conduit will be buried 18 inches deep.

Don't use EMT underground.
 
 