One side of double breaker won't reset
Hello all.
I have a double (tandem) breaker with 20A each. The top 20A breaker running my jacuzzi is working fine. However, the bottom 20A breaker that running my bathroom light, bedroom light, and the outlet in the bedroom won't reset after the storm.
I have tried to swap the circuit breaker with the exact same breaker and it's doing the same thing on that line.
I have unplugged and turn off everything that are on the same line and the circuit breaker still won't reset.
I have turned the breaker off all the way and then turn it on. Once I turned it on, it automatically turn red showing it tripped immediately.
Please help
I have a double (tandem) breaker with 20A each. The top 20A breaker running my jacuzzi is working fine. However, the bottom 20A breaker that running my bathroom light, bedroom light, and the outlet in the bedroom won't reset after the storm.
I have tried to swap the circuit breaker with the exact same breaker and it's doing the same thing on that line.
I have unplugged and turn off everything that are on the same line and the circuit breaker still won't reset.
I have turned the breaker off all the way and then turn it on. Once I turned it on, it automatically turn red showing it tripped immediately.
Please help
#4
I have never seen a tandem breaker with the trip window.
It is now an Easter egg hunt to find the short. You will need to start opening boxes until you find it.
It is now an Easter egg hunt to find the short. You will need to start opening boxes until you find it.
#5
Member
Thread Starter
Join Date: Apr 2016
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have never seen a tandem breaker with the trip window.
It is now an Easter egg hunt to find the short. You will need to start opening boxes until you find it
It is now an Easter egg hunt to find the short. You will need to start opening boxes until you find it
#6
Sound like I need to call the electrician to find the short
*Jbox closest to the breaker box may not be the first but often is and you have to start somewhere.
#9
Member
Thread Starter
Join Date: Apr 2016
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok I finally called an electrician and he was able to find the short wires but he can't fix my problem due to the wire is behind the wall. 
Anyways, I ran the new wire from the 1st receptacle to the next and everything works fine.
However, due to the location of it. I was unable to drill the holes through the 2x4 to run my new wire so I run the wire along the front of the 2x4. Do you think this will be a problem once I put the molding back?

Anyways, I ran the new wire from the 1st receptacle to the next and everything works fine.
However, due to the location of it. I was unable to drill the holes through the 2x4 to run my new wire so I run the wire along the front of the 2x4. Do you think this will be a problem once I put the molding back?

#11
Member
They way you ran the wire can be dangerous because it is so close to the surface.
I assume this is outer wall (which will be a load bearing wall) since I see some insulation.
The correct way to fix this is to cut the ceiling (or ceiling below) and do horizontal run in the ceiling.
Another option I can suggest is using wire channel and running wire outside of the wall. It can be painted to match your wall color if you want.
You can also run wire outside of your house using UF-b wire if you don't mind visible wire outside.
I assume this is outer wall (which will be a load bearing wall) since I see some insulation.
The correct way to fix this is to cut the ceiling (or ceiling below) and do horizontal run in the ceiling.
Another option I can suggest is using wire channel and running wire outside of the wall. It can be painted to match your wall color if you want.
You can also run wire outside of your house using UF-b wire if you don't mind visible wire outside.