expert opinion please on new HW heater install
#1
Member
Thread Starter
Join Date: May 2012
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
expert opinion please on new HW heater install
I am installing a new 20 gallon electric hot water heater in our small seasonal cottage.
The watts listed for the Rheem unit are 2000 watts. My plan is to run a new circuit from the breaker box (30 ft away) of romex 10/2, and add a single pole 30 amp switch, located above the new tank (120 volt install) to allow temporarily turning off the HW heater.
The tank will be located in the bathroom, adjacent to a sink, toilet, and shower. I am concerned about the safety aspect of the electric hot water heater, and am considering, as an added precaution, a 30 amp GFI circuit breaker at the breaker box.
Experts, any dangerous flaws in my plan? Is this overkill? Suggestions? Thanks!
The watts listed for the Rheem unit are 2000 watts. My plan is to run a new circuit from the breaker box (30 ft away) of romex 10/2, and add a single pole 30 amp switch, located above the new tank (120 volt install) to allow temporarily turning off the HW heater.
The tank will be located in the bathroom, adjacent to a sink, toilet, and shower. I am concerned about the safety aspect of the electric hot water heater, and am considering, as an added precaution, a 30 amp GFI circuit breaker at the breaker box.
Experts, any dangerous flaws in my plan? Is this overkill? Suggestions? Thanks!
#3
Forum Topic Moderator
I had a trailer yrs ago that had an 18 gallon 120 volt water heater but if I remember correctly it was on a 20 amp fuse. I'd be inclined to install a more efficient 240 volt heater and maybe step it up to 30 gallon - or are there space constrictions? Not sure what the safety worries would be as long as everything is wired up properly.
#4
The math says it is on the border line for a 20 amp breaker. Going with 10-2 will future proof the installation for a larger unit and is okay but I'd try a 20 amp breaker first. What breaker size is suggested on the label?
#5
Member
Thread Starter
Join Date: May 2012
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ray2047, the Rheem documentation seems to suggest (for 120 volts) 25 amp breaker and 10/2 wire.
marksr, the safety worries deal with nearby water, someone turning the HW heater on or off using the single pole switch (rather than the breaker)...just an extra peace of mind...perhaps this is overkill?
stickshift, yes, it seems it can be wired 120...
I am definitely not a pro electrician, just a novice amateur...leaning towards overkill if needed, for peace of mind.
thanks
marksr, the safety worries deal with nearby water, someone turning the HW heater on or off using the single pole switch (rather than the breaker)...just an extra peace of mind...perhaps this is overkill?
stickshift, yes, it seems it can be wired 120...
I am definitely not a pro electrician, just a novice amateur...leaning towards overkill if needed, for peace of mind.
thanks
#7
someone turning the HW heater on or off using the single pole switch (rather than the breaker)
#10
A pullout A/C disconnect will be cheaper than the toggle switch.
Shop Cooper Wiring Devices 30-Amp White Light Switch at Lowes.com
#11
Disconnect wiring note: If you use an A/C disconnect it is 2-pole but on 120 volt you only use one pole. You will only connect the hot. The neutral will be spliced through.
#12
Member
Disconnect wiring note: If you use an A/C disconnect it is 2-pole but on 120 volt you only use one pole. You will only connect the hot. The neutral will be spliced through.
#14
As long as the disconnect is non-fusible I don't believe it would be a code violation as long as both grounded and ungrounded conductors are disconnected simultaneously. Generally the neutral or grounded conductor is never opened at a disconnect except for in the case of gas pumps when it is required for the neutral conductor to also be disconnected.