Upsizing wire run to generator inlet ?

Reply

  #1  
Old 05-10-16, 09:38 AM
P
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 301
Received 0 Votes on 0 Posts
Upsizing wire run to generator inlet ?

From the Transfer Switch out, it's approx 125-140 run between the inlet + cordage of the generator.

I was thinking about upsizing the wire to 8 AWG. However, the transfer switch *reliance 10 breaker*, has #10 wire feeding their bus bar.

Will I still get the benefit of using 8 wire, or will it need to be 8 Wire from Gen - all the way back to the bus bar
 
Sponsored Links
  #2  
Old 05-10-16, 10:11 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 23,781
Received 638 Votes on 588 Posts
You will get the reduced resistance/voltage drop by running larger wire but if your wire is sized properly to begin with the reduction might not be noticeable.
 
  #3  
Old 05-10-16, 10:23 AM
P
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 301
Received 0 Votes on 0 Posts
I'm not clear.
Is V drop mitigated with any larger wire in the run, or does it need to be ~larger~ from point a- b. Meaning the entire run from the generator back the wire that connects the bus bar on the transfer switch.

That's where I'm seeking clarity.

Hell, even reliance said, that my inlet cord could be 10 wire, and the long length run from the inlet to the switch can be my 8, and the small wire from that to the bus bar is 10 already, they we're saying I will still see benefit if it's a longer run.

I was the impression that it needed to be from ~endpoint to endpoint~
 
  #4  
Old 05-10-16, 10:44 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
Voltage drop is a function of amperage flow, wire size and wire length. Increasing the wire size WILL reduce voltage drop proportional to the length of the wire where the size has been increased.
 
  #5  
Old 05-10-16, 12:33 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
This is a simple to use voltage calculator. electrician2.com voltage drop calculator
 
  #6  
Old 05-10-16, 12:37 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 43 Votes on 41 Posts
A general rule of thumb without running a formal calculation suggests that circuits greater than 100' length will see a benefit from upsizing the wire. If you want to know exactly, we need the cable length, load in amps and voltage.

You also may see some stability benefit on the generator -- small units tend to have trouble regulating engine speed when a long cord is used.
 
  #7  
Old 05-11-16, 06:20 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,110
Received 81 Votes on 75 Posts
A short length e.g. pigtail of thinner wire used to fit the terminal hole or screw on the breaker or lug or bus bar will not impair the benefits of the fatter wire used on the long run to combat voltage drop.

The thinner wire just has to meet the "normal" size requirements for "normal" length runs such as 10 gauge copper for 30 amps.

If you really wanted to, you could figure the voltage drop over the portion of the circuit with the fatter wire and figure the voltage drop over the portion of the circuit with the thinner wire and add the numbers together.
 

Last edited by AllanJ; 05-11-16 at 06:50 PM.
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: