"Too much" for a 20 amp breaker?


  #1  
Old 05-22-16, 05:47 AM
L
Member
Thread Starter
Join Date: Oct 2015
Location: USA
Posts: 55
Received 0 Upvotes on 0 Posts
"Too much" for a 20 amp breaker?

My pool house/ shed is supplied with a 100 amp subpanel off the main. In addition to the pool equipment, I recently installed a 20 amp breaker for two interior GFI outlets that I installed with which I plan to power a small stereo receiver (2 channel 200 watts) and a small refrigerator (10 cubic ft).

I'd like to also add a small interior overhead light with a switch and two exterior wall lights with a switch as well. Would this be too much for the 20 amp breaker or should I run a separate 15 amp for the lights? I understand the 80% of 2400 watts etc. Just not sure I'm missing something?
 
  #2  
Old 05-22-16, 06:28 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,332
Received 877 Upvotes on 740 Posts
That should be fine to run on a 20 amp circuit.
 
  #3  
Old 05-22-16, 05:47 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
The 80 % is only for a continuous load of 3 hours or greater. Intermitant loads can be 100%.
 
 