Splicing wires together mid-air

Contractor is installing new a/c compressor alongside the house. He ran flexible metal conduit (MC) from the main panel in the house, through an unfinished basement and into a crawl space. Just before going through the rim joist he transitioned from MC to single strand #10 THHN and ran the single strands in water tight flexible conduit out to a disconnect box mounted on the side of the house. Where he transitioned from MC to single stand in the crawl space it looks like he spliced the wires together and wrapped them in electrical tape. He did not use a junction box. Is this acceptable?
 
  #2  
Old 06-15-16, 10:14 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,151
Received 427 Upvotes on 380 Posts
Nope, definitely not. All connections need to be in an approved junction box. Also, using electrical tape instead of wire nuts is pretty much a no-no.

The connections should be in a 4x4 metal box or similar. You should definitely have him redo it.
 
  #3  
Old 06-15-16, 10:16 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
  #4  
Old 06-15-16, 01:22 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Sounds like a hack job to me. Should have a junction box, wirenuts and proper transition fittings and anti-short bushings on the MC.
 
  #5  
Old 06-15-16, 01:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,998
Received 205 Upvotes on 179 Posts
Definitely needs to be fixed.
 
  #6  
Old 06-15-16, 05:55 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
Also - cables need to be secured/supported within 12" of box.
 
  #7  
Old 06-16-16, 02:30 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,881
Received 188 Upvotes on 168 Posts
He did not use a junction box.
I hope "He" is an air conditioning contractor and not an electrical contractor. Did "He" get a permit for the new condensing unit? Did "He" get a permit for the new electrical work? I hope the whole job will be inspected.
 
 