100amp Sub Panel for Pool Equipment

I would like to know what type and size of wire to run underground from my 200 amp house panel, 50' to the proposed 100amp sub panel which will serve my new pool equipment.

Also, I assume I will run four wires. What size PVC conduit?

Confirm, 18" cover?

I will use copper wire.

What size breaker in house panel?
 
  #2  
Old 07-04-16, 03:26 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Give us the full load amps of the pump and any other equipment and we can tell you the size breaker at the house and wire size. My guess would be 40a or 60 amp.
 
  #3  
Old 07-04-16, 05:09 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,670
Received 260 Upvotes on 221 Posts
Here's some choices..........
50A #8-8-8-10 THWN 1" PVC
60A #6-6-6-10 THWN 1" PVC
80A #4-4-4-8 THWN 1.25" PVC
100A #3-3-3-8 THWN 1.25" PVC

Conduit I listed is actually a little larger than required for the #8, 6, and 4, but easier to pull through. 18" of cover is good for normal non traffic areas.
 
  #4  
Old 07-04-16, 07:08 PM
M
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks ray2047 & pattemp,

My pool contractor told me to get a 100amp sub panel which will be mounted on the exterior wall at the equipment pad.

That said, I counted up 85 amps +/-

1. 2 hp circ. pump
2. 140,000 btu heat pump
3. 1.5 hp spa air blower
4. Low voltage pool and landscape lighting. All led.
 
 