Eaton Type BR Quadplex breaker. Common trip vs independent trip?

Eaton Type BR Quadplex breaker. Common trip vs independent trip?


  #1  
Old 07-14-16, 05:20 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,783
Received 170 Votes on 146 Posts
Eaton Type BR Quadplex breaker. Common trip vs independent trip?

I was about to purchase a Type BR Quadplex breaker and found there are common trip and independent trip breakers.

I know common trip in 2 pole breakers mean both poles will trip at the same time and never seen independent trip in 2 pole breakers.

So, independent trip in quadplex means all 4 poles are independent or does it mean inner and outer poles are independent?

Does common trip quadplex trip all 4 poles ?
 
  #2  
Old 07-15-16, 06:00 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,790
Received 79 Votes on 71 Posts
A handle tie on two full size single pole breakers gives you an independent trip two pole solution.

Quadraplex BR common trip has each two pole configured as common unto itself. One of the two pole will trip both poles but leave the other alone.
 
  #3  
Old 07-15-16, 09:08 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 45 Votes on 43 Posts
I've seen different configurations, the most common one is that the center two poles are common trip and the outside two poles are independent trip. The center poles could be used for a 240V circuit and the outer poles could be used for separate circuits or a MWBC if you leave the included handle tie in place.
 
  #4  
Old 07-15-16, 04:35 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,783
Received 170 Votes on 146 Posts
A handle tie on two full size single pole breakers gives you an independent trip two pole solution
I wonder where would you want independent trip with handle tie. May be for a subpanel?

So, it seems what I want is a common trip breaker.


the most common one is that the center two poles are common trip and the outside two poles are independent trip.
What I need is 2 240V circuit. So, the one I'm getting has a handle tie between middle 2 and a handle tie between outer 2.
 
  #5  
Old 07-15-16, 06:06 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,147
Received 163 Votes on 146 Posts
I believe the independent trip quad is a BQ and the common trip quad is a BQC. I'd also recommend the common trip quad for your purposes. Personally, I'd avoid quads and tandems unless I had no other choice.
 
  #6  
Old 07-15-16, 06:59 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,783
Received 170 Votes on 146 Posts
I'd avoid quads and tandems unless I had no other choice.
I agree, mainly due to availability and the price.
But, I have no choice because there are no remaining space. It is going in to 6 space 12 circuit panel and 4 tandems are in use. Regular 30A 2 pole breaker is taking remaining 2 spaces and I need to add another 30A 2 pole circuit.
Getting BQC230230.
 
 