When we try and run three appliances the circuit breaker cuts off (15 amps). Could I just change and increase the breaker size go one size greater? Could I just replace it with 20 amps?
Kitchen can only run two appliances or less? Then circuit Breaks.
Old 08-10-16, 07:59 AM
C
Received 2 Votes on 2 Posts
No, you cannot just increase the size of the breaker. Breakers are sized to protect the size wire that was used to install the circuit. Increasing a breaker beyond the size appropriate for the wire used creates a real fire hazard.
Codes today call for two 20 amp small appliance circuits in kitchens just because so many appliances are used these days.
Most likely the best solution for you would be to install or have installed another circuit or two powering additional receptacles.
P
Received 629 Votes on 581 Posts
NO!!! You may not simply install a larger sized breaker.
A larger breaker may be installed if a certified electrician determines the size of ALL the wiring on that circuit. If you have 14ga wire anywhere in the circuit you must have a 15 amp breaker max. If the electrician finds that the entire circuit is wired with #12 wire then they could replace the breaker with a 20amp.
Yes, if your kitchen has a 15 amp circuit you may only be able to run two items at once. If there is a high draw item like a coffee maker brewing or a toaster oven you may only be able to run that one item.
Old 08-10-16, 11:14 AM
I
Received 43 Votes on 41 Posts
That's normal and expected behavior. Three appliances draw more power than a 15A circuit can provide. You either need another circuit added to the kitchen from the main panel box or to use fewer appliances at the same time. If you increase the breaker size it will be a fire hazard by allowing too much power on the #14 gauge wire running to the kitchen.
Old 08-10-16, 03:55 PM
pcboss's Avatar
Received 87 Votes on 74 Posts
Try to see if there is another breaker for the kitchen. Two circuit have been required for quite a while.
Old 08-11-16, 07:45 PM
biketrax's Avatar
WILL DO!! Even 68 year old house??
Thanks for all the quick responses!!
Old 08-12-16, 12:44 AM
pcboss's Avatar
I doubt it goes back that far, but it will not cost anything to check.