no power in part of circuit


  #1  
Old 09-14-16, 06:43 PM
G
Member
Thread Starter
Join Date: Nov 2005
Location: Canada
Posts: 80
Upvotes: 0
Received 0 Upvotes on 0 Posts
no power in part of circuit

Problem and history in point form:-
--- the fuse ( screw type ) is ok
--- part of the circuit has power while the further part has none.
--- the house is a side split
--- I trace the wires in the crawl space and in the attic
--- the light switch in the living room has voltage but the light does not come on
--- the house is over 50 years old in Ontario, Canada
--- the problem started less than a year ago.
--- no electrical work was done to cause the problem
--- the problem started on and off - that is, there was no power and after a while it fixed itself
--- now it is just no power
What could be the cause?

Ghelp
 
  #2  
Old 09-14-16, 06:50 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I trace the wires in the crawl space and in the attic
--- the light switch in the living room has voltage but the light does not come on
How did you determine there was power? Common mistakes in doing this is measuring across the switch and using a non contact tester.
What could be the cause?
A bad connection. The connection could be at the last working outlet (outlet=light or switch or receptacle) or the first non working outlet. Any wires inserted in the back of a device needs to be moved to the screws. Any wirenuts need to be redone. Ant screw connections need to be tested for tightness.
 
 