Washer, dryer and sump pump on same circuit?
#1
Member
Thread Starter
Washer, dryer and sump pump on same circuit?
Can I put a washer, electric dryer, and a sump pump on the same DEDICATED 20 amp branch circuit?
-With a home run to panel with single individual surface mounted boxes in basement.
GFI necessary?
-With a home run to panel with single individual surface mounted boxes in basement.
GFI necessary?
#5
Member
GFCI necessary for the 120v washer and pump receptacles. Spend the bucks and get one of the GFCIs that sound an alarm if tripped.
#6
A sump pump may not be hard wired into the so called laundry area branch circuit but nothing prevents you from plugging in a sump pump into a receptacle in the laundry room.
You may want to find out the maximum (starting) power draw for the washer, the gas dryer, and the sump pump. If these all together exceed 20 amps then you should not plug them all into the same circuit.
You could call the manufacturers, or you could buy a little gadget the you plug the appliance into and the gadget plugs into the wall. One such gadget is called Kill-A-Watt. It may require several tries since the device spot checks the current draw every few seconds and may or may not miss the peak draw which only lasts a few seconds.
I'm pretty sure that an all electric dryer, even if 120 volts, will max out the circuit all by itself so nothing else should be plugged into that circuit.
Although higher amperage 120 volt branch circuits can be created, the washer and the sump pump may not be plugged into a circuit of greater than 20 amps.
You may want to find out the maximum (starting) power draw for the washer, the gas dryer, and the sump pump. If these all together exceed 20 amps then you should not plug them all into the same circuit.
You could call the manufacturers, or you could buy a little gadget the you plug the appliance into and the gadget plugs into the wall. One such gadget is called Kill-A-Watt. It may require several tries since the device spot checks the current draw every few seconds and may or may not miss the peak draw which only lasts a few seconds.
I'm pretty sure that an all electric dryer, even if 120 volts, will max out the circuit all by itself so nothing else should be plugged into that circuit.
Although higher amperage 120 volt branch circuits can be created, the washer and the sump pump may not be plugged into a circuit of greater than 20 amps.
Last edited by AllanJ; 09-21-16 at 04:50 PM.
#7
I'm seeing this as a washer, gas dryer, and sump pump.
Could you run them on one circuit..... the short answer is yes.
If you have a critical sump pump where it runs a lot and could overflow easily.... you'd be better advised to put the sump pump on its own circuit.
Could you run them on one circuit..... the short answer is yes.
If you have a critical sump pump where it runs a lot and could overflow easily.... you'd be better advised to put the sump pump on its own circuit.
#9
I'm seeing this as a washer, gas dryer, and sump pump.