How to 'break out' multiple circuits in a single conduit??

How to 'break out' multiple circuits in a single conduit??

Reply

  #1  
Old 10-05-16, 11:22 PM
U
Member
Thread Starter
Join Date: Oct 2016
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
How to 'break out' multiple circuits in a single conduit??

I'm running 3 20 amp circuits in a single 1/2'' EMT conduit.

What is the best way to 'break out' the circuits from single conduit into 3 separate conduits that will then be connected to outlets?

My current plan is to run the 1/2'' conduit into a junction box and simply pull each circuit through a separate exit point on the junction box and then have each circuit continue individually an outlet.

Is this an acceptable way of achieving the above?

Thanks!
 
Sponsored Links
  #2  
Old 10-06-16, 07:53 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,668
Received 223 Votes on 196 Posts
If you are using EMT, it is continuous and assembled with the proper fittings, you do not need a grounding conductor. You can use one if you choose.

For me, it will depend on how I run the conduit. Most cases I just run the conduit to the first outlet box and drop one circuit, then run to the next box and drop circuit 2, and so on. Example:
-------[1]--------[2]--------[3]

However, your method is OK too. Whatever works beast for your project.
 
  #3  
Old 10-06-16, 08:33 PM
U
Member
Thread Starter
Join Date: Oct 2016
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Thank you very much for the replies.

Is there any negative to running a separate ground for each circuit?

The reason I ask is that I've purchased stranded 12 gauge wire for the project and I don't mind running the extra grounds if it won't cause a problem.

Thanks again for your insight.
 
  #4  
Old 10-06-16, 08:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,855
Received 1,203 Votes on 1,113 Posts
You're only allowed by code to put ten #12's in a 1/2" conduit.

Figuring three wires per circuit would give you nine conductors.
The only problem is that the grounds get connected together and to the box.
You're going to wind up with a lot of unnecessary ground wire.

It would be beneficial to keep it to one common ground thru the run.
 
  #5  
Old 10-07-16, 04:19 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,668
Received 223 Votes on 196 Posts
According to my, book you can only get 9 #12 THHN wires in 1/2" EMT.
 
  #6  
Old 10-07-16, 04:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,855
Received 1,203 Votes on 1,113 Posts
I know...there's always a discrepancy.
My one book shows 10 and the other shows 9 in EMT with 10 in IMC. Go figure.
 
  #7  
Old 10-07-16, 05:24 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,668
Received 223 Votes on 196 Posts
My book is the NEC tables in the back. It shows 10 for 1/2" IMC. Humm.

We could do it the long way:
EMT area for more then two wires (40%) = .122 inches
IMC area for more then two wires (40%) = .137 inches
Area of one #12 THHN wire = .0133
9 x .0133 = .1197
10 x .0133 = .133

The math checks out.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: