GFCI trips when reading voltage

Not sure what's going on, but when I check voltage in this circuit to ground reference, the gfci trips. If I check voltage to neutral reference, it does not.

Basically, why would simply trying to read voltage trip a gfci?
 
  #2  
Old 11-26-16, 10:23 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,451
Received 4,051 Upvotes on 3,634 Posts
Welcome to the forums.

Basically, why would simply trying to read voltage trip a gfci?
A GFI measures the inbalance between hot and neutral. So if you test from hot to ground with a heavy enough load.... the GFI will trip due to the hot/neutral inbalance.
 
  #3  
Old 11-27-16, 05:31 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,399
Received 893 Upvotes on 754 Posts
GFCI's that are for protection of personnel (standard GFCIs) will trip on 4-6 milliamps. The GFCI is doing exactly what it is supposed to do.
 
  #4  
Old 11-27-16, 12:19 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,560
Upvotes: 0
Received 285 Upvotes on 260 Posts
The act of reading a voltage draws a small amount of current.

A typical digital voltmeter draws a much smaller current than a typical analog (swinging needle) voltmeter where the latter might draw enough to trip the GFCI unit.
 
 