Replace Old ITE Imperial

Going to replace my old breaker panel(1972) with a Homeline SQ-D 125a equivalent. I'll keep it simple.

Because previous owners put incorrect breakers in there, tandems where tandems don't belong. There is some charring on some of the bus bar connectors. I removed those breakers and have empty space now.

Service(main) panel has 125a disconnect that connects to panel I am replacing via about 130' of 2/0 2/0 2/0(bare) al SER. Technically means it is a sub panel.

Question is can I just swap it out and keep the existing 3 wire system and let the neutrals and grounds share bonded bars and not isolate them (and leave out the green bonding screw) because this was the original design. I know it not is good as a 4 wire, but is it legal and safe( I know the new panel with be safer by defacto). If i need to add the 4th wire can it be a solo, or do I need to replace the whole thing with a 2/0-3 + ground? I have put in plenty of new sub's and always used 4 wire, but first time replacing an older panel.
 
  #2  
Old 12-06-16, 05:11 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
Service(main) panel has 125a disconnect that connects to panel I am replacing via about 130' of 2/0 2/0 2/0(bare) al SER. Technically means it is a sub panel.
Yes, that is a subpanel and the SER feeder is a 4-wire feeder. SER cable has 3 insulated conductors and 1 bare grounding conductor.

Question is can I just swap it out and keep the existing 3 wire system and let the neutrals and grounds share bonded bars and not isolate them (and leave out the green bonding screw) because this was the original design.
Your question makes no sense. What 3-wire system, you have a 4-wire SER cable feeder. The panel you are changing is in the same building as the 125 amp disconnect.....right?
 
  #3  
Old 12-06-16, 06:19 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,920
Received 175 Upvotes on 153 Posts
Can you post a picture of the panels in question ?
 
  #4  
Old 12-14-16, 06:22 AM
A
Member
Thread Starter
Join Date: Apr 2005
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
I guess that was misleading. The Bare wire is the same size as the 2 mains, not smaller as the in the some bare(grounds), but there is only 3 wires. Here is the pic. And correction it is a 100amp breaker in the main and I am not going to swap that. Here is a pic.
Name:  EB.jpg
Views: 1133
Size:  51.4 KB
 
  #5  
Old 12-14-16, 01:29 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
This is up to the local inspector. Sometimes on what is strictly a panel swap (no increase in amps) and no change of the other service components, they will not make you replace the 3 wire feeder as it would be grandfathered as part of the original installation.

If you do need to install a new feeder, you would need to replace the entire cable with a four-conductor cable.
 
  #6  
Old 12-15-16, 01:55 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
Service(main) panel has 125a disconnect that connects to panel I am replacing via about 130' of 2/0 2/0 2/0(bare) al SER. Technically means it is a sub panel.
There is the problem, that isn't SER cable, but SEU cable.
 
 