Six Breaker Rule/Disconnect
#1
Six Breaker Rule/Disconnect
Some in the past here have posted the 6-breaker rule applies to the actual number of installed breakers other have said no it is the number of circuits a box is rated for even if six breakers or less are installed. Looking on the net it gets very confusing and I know in the end it is the local AHJ's call but just wondering what the pros here think.
Last edited by ray2047; 02-02-17 at 08:56 PM.
#3
Well, even on that other electrical only Forum with the initials MH, they have some lively discussions of the same issue. Most went with what's installed, but a few went with what COULD be installed.
I guess you need to know your inspectors preferences.
I guess you need to know your inspectors preferences.
#5
I have never thought it was the number of breakers in an enclosure,but rather the number of operations to disconnect a service.
Copied from '14 “230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or in switchgear. There shall be not more than six sets of disconnects per service grouped in any one location.”
Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected by copyright.
Check out this book on the iBooks Store: https://itun.es/us/elMFQ.l
Copied from '14 “230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or in switchgear. There shall be not more than six sets of disconnects per service grouped in any one location.”
Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected by copyright.
Check out this book on the iBooks Store: https://itun.es/us/elMFQ.l
#6
I agree that the standard should be applied to what is actually installed. Any future uses would be covered by a new design, permit and inspection which, at that time, would identify any code problems created by the proposed work including service limitations. Further there is no reason a "service" needs to be a factory-built breaker panel other than it's convenient to do it that way. A wiring gutter and collection of fuse holders can be a service per code, and that is infinitely expandable.
#8
Hi Ray, what is the code rule you are referring to? I thought it was for service disconnects please correct me.
Geo
Geo
#10
I thought it was for service disconnects please correct me.
#11
A means of disconnect is required at detached structures if served by a feeder and not a multiwire or single circuit. Seems that the same rule as as service is applied.
#13
225.33 Maximum Number of Disconnects.
(A) General. The disconnecting means for each supply
permitted by 225.30 shall consist of not more than six
switches or six circuit breakers mounted in a single enclo-
sure, in a group of separate enclosures, or in or on a switch-board. There shall be no more than six disconnects per
supply grouped in any one location.
(A) General. The disconnecting means for each supply
permitted by 225.30 shall consist of not more than six
switches or six circuit breakers mounted in a single enclo-
sure, in a group of separate enclosures, or in or on a switch-board. There shall be no more than six disconnects per
supply grouped in any one location.
You will be limited to six circuits if you don't use a disconnect for the feed to the panel even if there is room for more circuits.
#14
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,626
Received 241 Upvotes
on
205 Posts
You will be limited to six circuits if you don't use a disconnect for the feed to the panel even if there is room for more circuits.
#15
Thanks. I originally wrote breakers but then I thought some would think two handle tied breakers were counted as two breakers. Trying to keep the explanation as simple ans short as possible for newbies but breakers has a good ring to it.
#16
I am in the what is "currently installed" camp. Any modifications done to the wiring would be required to follow any codes that apply at that time.