Six Breaker Rule/Disconnect

Some in the past here have posted the 6-breaker rule applies to the actual number of installed breakers other have said no it is the number of circuits a box is rated for even if six breakers or less are installed. Looking on the net it gets very confusing and I know in the end it is the local AHJ's call but just wondering what the pros here think.
 

Last edited by ray2047; 02-02-17 at 08:56 PM.
  #2  
Old 02-02-17, 08:19 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
I am on the side of what is installed , not future usages.
 
  #3  
Old 02-02-17, 10:06 PM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 19,281
Received 5 Upvotes on 5 Posts
Well, even on that other electrical only Forum with the initials MH, they have some lively discussions of the same issue. Most went with what's installed, but a few went with what COULD be installed.

I guess you need to know your inspectors preferences.
 
  #4  
Old 02-02-17, 11:05 PM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Yes, I checked MH before posting this and saw both sides represented.
 
  #5  
Old 02-03-17, 05:33 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
I have never thought it was the number of breakers in an enclosure,but rather the number of operations to disconnect a service.
Copied from '14 “230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or in switchgear. There shall be not more than six sets of disconnects per service grouped in any one location.”

Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected by copyright.

Check out this book on the iBooks Store: https://itun.es/us/elMFQ.l
 
  #6  
Old 02-03-17, 06:54 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
I agree that the standard should be applied to what is actually installed. Any future uses would be covered by a new design, permit and inspection which, at that time, would identify any code problems created by the proposed work including service limitations. Further there is no reason a "service" needs to be a factory-built breaker panel other than it's convenient to do it that way. A wiring gutter and collection of fuse holders can be a service per code, and that is infinitely expandable.
 
  #7  
Old 02-03-17, 07:14 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,757
Received 676 Upvotes on 573 Posts
I am in the what is "currently installed" camp. Any modifications done to the wiring would be required to follow any codes that apply at that time.
 
  #8  
Old 02-04-17, 04:30 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi Ray, what is the code rule you are referring to? I thought it was for service disconnects please correct me.
Geo
 
  #9  
Old 02-04-17, 05:23 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,757
Received 676 Upvotes on 573 Posts
You sited the correct code reference Geo.
 
  #10  
Old 02-04-17, 11:18 AM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I thought it was for service disconnects please correct me.
Yes and that adds to my confusion. It is often used here including by me referring to subpanels in detached structures and I was trying to find out if I was misinformed.
 
  #11  
Old 02-04-17, 11:32 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
A means of disconnect is required at detached structures if served by a feeder and not a multiwire or single circuit. Seems that the same rule as as service is applied.
 
  #12  
Old 02-04-17, 04:07 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,626
Received 241 Upvotes on 205 Posts
The requirement for a disconnect at other structures supplied by a feeder is covered under NEC 225 II, Sections 225.31, 32, & 33.
 
  #13  
Old 02-04-17, 05:41 PM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
225.33 Maximum Number of Disconnects.
(A) General. The disconnecting means for each supply
permitted by 225.30 shall consist of not more than six
switches or six circuit breakers mounted in a single enclo-
sure, in a group of separate enclosures, or in or on a switch-board. There shall be no more than six disconnects per
supply grouped in any one location.
Strict interpretation I would say is at the time of inspection and means even if more than six breakers can be used you are limited to six breakers till you add another means of disconnect. I use to write it that way in answers but was occasionally "corrected". I will just make myself more clear in the future. Such as:
You will be limited to six circuits if you don't use a disconnect for the feed to the panel even if there is room for more circuits.
 
  #14  
Old 02-05-17, 06:44 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,626
Received 241 Upvotes on 205 Posts
You will be limited to six circuits if you don't use a disconnect for the feed to the panel even if there is room for more circuits.
I would not say circuits because someone could use multibranch circuits and have 12 circuits with using only 6 double pole beakers. A double pole or two singles with a handle tie is considered one switch. I'd say "Breakers".
 
  #15  
Old 02-05-17, 08:22 AM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Thanks. I originally wrote breakers but then I thought some would think two handle tied breakers were counted as two breakers. Trying to keep the explanation as simple ans short as possible for newbies but breakers has a good ring to it.
 
  #16  
Old 02-05-17, 09:44 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
I am in the what is "currently installed" camp. Any modifications done to the wiring would be required to follow any codes that apply at that time.
The several jurisdictions I am familiar with interpret the code just the opposite and go by the number of breakers that "COULD" be installed and not what actually is installed at time of final inspection. That could perhaps be what they viewed as the intent of the code. I believe they were also always afraid someone would come along and install more circuits without a permit/inspection. Let's face it, a ton of electrical work is installed every day with no permit/inspection. For that reason, I have always gone that way, but I will agree that the code doesn't specifically say that the enclosure must not be able to accept more than 6 breakers.
 
 