Should I use a dedicated circuit for a towel warmer?


  #1  
Old 02-24-17, 09:10 AM
B
Member
Thread Starter
Join Date: Feb 2017
Location: USA
Posts: 8
Likes: 0
Received 0 Likes on 0 Posts
Should I use a dedicated circuit for a towel warmer?

I purchased a 120 volt (70 watt) towel warmer that will be hard wired into our bathroom. I have 12-2 wire on a 20AMP breaker already in there that will be used for outlets and lighting.

Should I run a dedicated line for the towel warmer or can I use what's already there?

This is the towel warmer I purchased: 24" Keegan Hardwired Towel Warmer - Bathroom

Thanks!
 
  #2  
Old 02-24-17, 09:59 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Likes: 0
Received 15 Likes on 13 Posts
Not needed since it uses less amps than some incandescent light bulbs.
 
  #3  
Old 02-24-17, 11:15 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,868
Received 221 Likes on 188 Posts
If that towel warmer is placed where it can be reached from the shower or tub I'd take power off the load side of a GFCI outlet. Actually I'd take the power off the load side of a GFCI outlet regardless of where it's mounted in the bathroom.
 
  #4  
Old 02-25-17, 08:01 AM
W
Member
Join Date: Feb 2006
Location: USA
Posts: 6,920
Received 57 Likes on 50 Posts
Amperage

70 watts/120 volts = .58 amps.
 
 