100amp service tripping
Hello,
My detached garage has a separate panel that runs from the house. It is a 100amp service.
When out in the garage it seems when I have the 1500watt heater going (on a 30amp circuit) and when I run tools(no particular one and not always) it will trip the 100amp breaker in the house. When I come in to flip it back there is an odd smell as well associated with the trip.
I have run my table saw with dust collection going and my air circulator for example and not tripped this. It always seems to happen if I have the heater on that it will trip the 100amp breaker. Today I had music going, the heater small shop vac attached to my chop saw and when I fired up the chop saw and started in on my cut did I trip.
It always trips it in the house and seems to always have the smell associated with it.
Any ideas what might be causing this? Is this the heater where the issue reisides?
Why also does it only trip it inside?
Any help would be great.
Thanks.
My detached garage has a separate panel that runs from the house. It is a 100amp service.
When out in the garage it seems when I have the 1500watt heater going (on a 30amp circuit) and when I run tools(no particular one and not always) it will trip the 100amp breaker in the house. When I come in to flip it back there is an odd smell as well associated with the trip.
I have run my table saw with dust collection going and my air circulator for example and not tripped this. It always seems to happen if I have the heater on that it will trip the 100amp breaker. Today I had music going, the heater small shop vac attached to my chop saw and when I fired up the chop saw and started in on my cut did I trip.
It always trips it in the house and seems to always have the smell associated with it.
Any ideas what might be causing this? Is this the heater where the issue reisides?
Why also does it only trip it inside?
Any help would be great.
Thanks.
#2
Only the sub panel breaker is tripping..... not the house main.... correct ?
It sounds like a defective 100A breaker as it's tripping prematurely.
It may also be a loose connection where that breaker attaches to the bus bars in the main panel.
It sounds like a defective 100A breaker as it's tripping prematurely.
It may also be a loose connection where that breaker attaches to the bus bars in the main panel.
#3
Member
Thread Starter
Join Date: Feb 2005
Location: US
Posts: 352
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the quick reply.
The house breaker is NOT tripping. It is only the house 100 amp breaker that is tripping.
So you think that smell is probably the breaker?
The house breaker is NOT tripping. It is only the house 100 amp breaker that is tripping.
So you think that smell is probably the breaker?
#4
It is only the house 100 amp breaker that is tripping.
So you think that smell is probably the breaker?
So you think that smell is probably the breaker?
#5
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
There are a few statements from the original poster that need clarification.
The word service has a very specific definition in electrical work. It is the point where the utility's wiring ends and the customer's wiring begins. It generally includes the overhead drop or underground lateral, the meter and the main circuit breaker. If the OP means he has a 100 ampere circuit breaker in his service panel (the main panel containing the main circuit breaker) feeding the circuit to the garage that would be a 100 ampere feeder, not a service.
So, what is the SERVICE main circuit breaker rating?
What voltage is this heater? Is it plugged in or hard-wired? 1500 watts at 120 volts should be on a 20 ampere circuit and if it is 240 volts then it should be on a 15 ampere circuit. If it is a plugged in heater (not hard-wired) then the circuit cannot be more than 20 amperes unless it has a special plug/receptacle precluding using the receptacle as a general purpose receptacle.
My detached garage has a separate panel that runs from the house. It is a 100amp service.
So, what is the SERVICE main circuit breaker rating?
... I have the 1500watt heater going (on a 30amp circuit)...
#6
Member
Thread Starter
Join Date: Feb 2005
Location: US
Posts: 352
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the responses and it seems like an easy thing to replace the breaker and try that.
@Furd, lets see if i can clarify this information best I can. I will include a picture of the panel in the house where the breaker is tripping. Perhaps i should have used sub panel? The garage simply has a break from the main panel in the house as you can see powering it. Does that help?
I think this is the heater being used or a very similar model.
https://www.northerntool.com/shop/to...VkYaAl3s8P8HAQ
It was from Northern tool some years ago and has a very similar plug to the one this one requires as well. 6-30p. Does that help @Furd and does that help others too verify a bit better if there was any uncertainty that I should try and replace the breaker firs?
Thanks again.
Picture of house panel and pointing at breaker that is tripping
@Furd, lets see if i can clarify this information best I can. I will include a picture of the panel in the house where the breaker is tripping. Perhaps i should have used sub panel? The garage simply has a break from the main panel in the house as you can see powering it. Does that help?
I think this is the heater being used or a very similar model.
https://www.northerntool.com/shop/to...VkYaAl3s8P8HAQ
It was from Northern tool some years ago and has a very similar plug to the one this one requires as well. 6-30p. Does that help @Furd and does that help others too verify a bit better if there was any uncertainty that I should try and replace the breaker firs?
Thanks again.
Picture of house panel and pointing at breaker that is tripping
#7
Even the specifications of the heater call for a 20 amp overcurrent protection, so at 30 amps, it could be heating up too much. I would check/change the 100 amp house breaker. What size breaker do you have in the garage, or is it a lug panel? Can we see a picture of the inside of that sub panel?
#8
Member
Join Date: Nov 2007
Posts: 295
Upvotes: 0
Received 0 Upvotes
on
0 Posts
He was being a little nitpicky as far as the terms.. It's pretty clear from what you said in the post that the garage has a subpanel.
So yeah if it has the same plug as that, it requires a 30A circuit but it's only drawing 20A. And that being the case, not knowing the size of your dust collector (assuming it's not a huge one, maybe the 2HP Harbor Freight one?) it's doubtful you're using over 80A between everything else to trip that breaker. Just go ahead and replace it.
No, it says it draws 20A. It comes with a 6-30P, which means it requires a 30A circuit.
So yeah if it has the same plug as that, it requires a 30A circuit but it's only drawing 20A. And that being the case, not knowing the size of your dust collector (assuming it's not a huge one, maybe the 2HP Harbor Freight one?) it's doubtful you're using over 80A between everything else to trip that breaker. Just go ahead and replace it.
Even the specifications of the heater call for a 20 amp overcurrent protection, so at 30 amps, it could be heating up too much
#9
Before changing the breaker..... turn it off and remove it from the panel. Look at the clips on the back of the breaker. Make sure they aren't discolored. Check to make sure the two screw terminals on the breaker are also tight.
Any connection heat can cause the breaker to trip prematurely.
Any connection heat can cause the breaker to trip prematurely.
#12
A 1500 watt heater cannot draw 20 amps, let alone enough to require that 30 amp plug. Even if considered a continuous load it is less than 16 amps at 120.