Weatherproof Outlet Install

i want to install a weatherproof outlet on the outside of a shed, the shed itself contains a sub-panel inside so power will be coming from there. Not sure what is needed to get the wiring from inside to outside receptacle in terms of conduit, etc. I have some flexible non-metallic 1/2" pvc but unsure how to connect that to the weatherproof box kit I purchased (it has a couple of threaded ports but the conduit fittings appear meant for a knock out). What is typical approach in this scenaro?
 
  #2  
Old 09-17-17, 06:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
If the receptacle is close to the panel..... just use cable.

The box will have 1/2" threaded hubs. That flex cable should have 1/2" threaded fittings with nuts. Take the nut off and screw the fitting directly into the box. The picture shows one type of flexible conduit.
 
Attached Images  
  #3  
Old 09-17-17, 06:50 PM
R
Member
Thread Starter
Join Date: Oct 2008
Location: Great White North
Posts: 195
Received 1 Upvote on 1 Post
Ok great, I was hoping to be able to do something l like that. Thanks PJMax!!
 
 