ok here it is.

I have my main outdoor 200amp panel (its full) so I bought a 100amp sub panel which is mounted on the back of the same utility pole.
I have 3 gauge wire to run from a a 100amp breaker in my main box to feed the sub panel.

so I just bought and had placed a 12x24 shed about 60ft away from my utility pole that will be a in law suite and it already has a 125 amp service panel in it.

so from the 100 amp “sub panel” (connected directly from my main panel) to this new sub panel in the shed can I run 8/3 wire for 60ft to power the sub panel or is that not big enough gauge wire?

what will be running in the new shed:

1) small apartment size stove
2) small apartment size refrigerator
3) 1 12k btu window unit (9.19 amps)
4) 6 outlets (3 gfi)
5) 2 interior lights and one outside light

I put in a tankless water heater but that is being wired directly to the 100amp service panel next to my main panel on its own breaker so won’t be connected to the shed sub panel at all.

let me know before I hook this 8/3 wire up.

thanks in advance
 
  #2  
Old 10-05-17, 02:19 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
#8 sounds a little light because that only gives you 40A. The water heater on it's own feed from the pole is not allowed. Only one feeder is allowed to serve power to an outbuilding.
 
  #3  
Old 10-05-17, 02:36 PM
C
Member
Thread Starter
Join Date: Nov 2013
Location: Usa
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
The water heater will be hooked up into my 200amp panel not the 100amp service panel so because that water heater wire is fed into the same direction as the main feed for the shed, that’s not allowed?
 
  #4  
Old 10-05-17, 02:44 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
Running two circuits to the shed is not allowed by the NEC. If the water heater is in the shed then it needs to get power from the subpanel that's in the shed.
 
  #5  
Old 10-05-17, 02:55 PM
C
Member
Thread Starter
Join Date: Nov 2013
Location: Usa
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok so if I include the water heater into the 100 amp service panel then with the other things mentioned that are in place with the 100amp be enough? If so then the feeder wire needs to be what 2 awg copper ran that 60ft?
 
  #6  
Old 10-05-17, 02:59 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
A 100A feed to the shed should be enough, but with that said, what's the power demand for the tankless water heater? #3 Cu or #1 Al is enough for 100A.
 
  #7  
Old 10-05-17, 03:10 PM
C
Member
Thread Starter
Join Date: Nov 2013
Location: Usa
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
220v 60amp 6/3 wire for the tankless water heater
 
  #8  
Old 10-05-17, 04:45 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
The 100A may be enough, but you need to figure what the total load could be at one time with the water heater going plus what ever else may be turned on at the same time. Is a heater ever needed?
 
  #9  
Old 10-05-17, 06:36 PM
C
Member
Thread Starter
Join Date: Nov 2013
Location: Usa
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well the stove calls for a 40amp breaker but no if a heater is ever used it will be a small space heater plugged in.

so the only thing that pulls high amps that could be running the same time as the water heater would be the stove which again is 40amp. I’m thinking I should get a 125amp sub panel to mount on the back side of the main panel cause the sheds sub panel is already 125amp but obviously was only ably to produce 100amp to it as of now.
 
  #10  
Old 10-06-17, 09:56 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,799
Received 175 Upvotes on 158 Posts
220v 60amp 6/3 wire for the tankless water heater

Am I correct in assuming the 6-3 is UF-B cable? This is really a moot point since as has been mentioned, you are only allowed one power feed to a detached structure.


let me know before I hook this 8/3 wire up.

Again, is this UF-B cable?
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: