Hot/Ground Reverse?
#1
Member
Thread Starter
Join Date: Oct 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hot/Ground Reverse?
Tried tracing a problem in my home where electrical outlets and lights decided to stop working, checked breaker and seen nothing wrong, wasnt tripped. I buy a Socket Tester and all the problematic outlets came back as Hot/GRD Reverse. I never could trace the problem to anything, I checked out light fixtures affected with a Voltage Detector Pen, it would give beeps indicating it was getting voltage, it seemed to be getting these readings on the entire circuit, I figured the GFCI was at fault but unsure, reset button dont work and my guess is because of the fault and it not getting correct power, it would even show as Hot/GRD Reverse. I am stumped on where this problem is, could the breaker be at fault due to it being only 15 AMP and it having to power as much as it is in the diagram I show? Prior to the failure, lights would flicker very lightly and constant which made me think it was a breaker gone bad, any suggestions? below is the diagram of whats on the circuit, whats in green is in between on another circuit that works.
#3
I buy a Socket Tester and all the problematic outlets came back as Hot/GRD Reverse. I never could trace the problem to anything, I checked out light fixtures affected with a Voltage Detector Pen,
#4
Missing neutral would cause the receptacles (and lights) to not work but still activate a proximity voltage detector.
Agree 100%. My experience when a plug-in receptacle tester indicates Hot-Grd Reverse that the problem has always been no neutral. Give that non-contact tester to your kids to play with, they are nothing much more than a toy, but they do generate a lot of profit for the big box home stores. They sell millions of them.
#7
Member
Thread Starter
Join Date: Oct 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Found problem. It was a burnt out ground in breaker panel. Crumbled in my hand when i removed it and cut it and put it back on.
Last edited by wwepatriot; 10-09-17 at 02:21 PM.
#8
It was a burnt out ground in breaker panel.
#14
Member
Join Date: May 2019
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Bad white wire
Weed trimmer stopped working; socket was dead (hot ground reverse on the plug-in tester), and several other sockets on that line, too.
The last "working" socket on that line was melted, and the white wire burnt!
The last "working" socket on that line was melted, and the white wire burnt!
#15
If only the end where it was attached to the bar or screw got burned then nothing wrongwith the circuit or wire, It was loose where it was attached and loose connections can get very hot even when the circuit load is much lower than the breaker rating.
While you are at it, tighten all of the other small screws and set screws in the panel. Flip off each breaker before touching the screw terminal(s) beside it, then flip it back on.
(Don't use extreme muscular strength to tighten screws.)
While you are at it, tighten all of the other small screws and set screws in the panel. Flip off each breaker before touching the screw terminal(s) beside it, then flip it back on.
(Don't use extreme muscular strength to tighten screws.)
#16
Member
Join Date: Jul 2020
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Another possible solution
Hello y’all! I know this thread is a bit old, but it served me as a guide to solve my Hot/Gnd Rev. In my case I traced it back to a CGFI receptacle I wired incorrectly. The leads were inverted. They were at the bottom (where the sticker on the receptacle states ”Only for use to power additional receptacles and switches”), and the additional receptacles and switches were connected to the top. Once I deciphered it, the tester no longer showed the Hot/Gnd Rev, and showed correct wiring. Hope it helps!