Wiring a shunt/ammeter into a 24v DC charger
#1
Member
Thread Starter
Join Date: Nov 2017
Location: Canada
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wiring a shunt/ammeter into a 24v DC charger
I have a home made 24 V DC charger using an alternator run by an old snowmobile motor. It is used to charge my battery bank of my solar system during those poor sun days of November.
I recently purchased on EBay a digital display with a 100 Amp shunt which I would like to insert in line to record the charge in amps. I am currently using the charger at idle speed so as not to create too much current, and am using a computer fan to cool the alternator.
Can anyone tell me how to wire this. Thanks
I recently purchased on EBay a digital display with a 100 Amp shunt which I would like to insert in line to record the charge in amps. I am currently using the charger at idle speed so as not to create too much current, and am using a computer fan to cool the alternator.
Can anyone tell me how to wire this. Thanks
#2
Welcome to the forums.
Model numbers or a picture would be good for confirmation.
Basic wiring of a shunt and ampmeter
Model numbers or a picture would be good for confirmation.
Basic wiring of a shunt and ampmeter
#3
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Shunts are normally wired into the negative conductor. This is especially true of the Chinese units and combination meters available on ebay.
Check out this page. https://www.google.com/search?q=wiri...w=1056&bih=652
Check out this page. https://www.google.com/search?q=wiri...w=1056&bih=652
#5
Member
Neg side monitor is prefered in a car, due to potential shorts to frame. In large plastic boats, I see a lot of + side monitoring.
I just did some shunt wiring last week for industry and it was in the pos side of an ungrounded 125V dc system that fed 20A motor.
I just did some shunt wiring last week for industry and it was in the pos side of an ungrounded 125V dc system that fed 20A motor.
#6
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
IF it is just a simple analog ammeter then yes, it WILL work in either lead.
BUT, the original poster stated: I recently purchased on EBay a digital display with a 100 Amp shunt...
The wiring on every single Chinese-made DIGITAL ammeter I have seen, and I have seen several, REQUIRED the shunt to be in the negative lead due to the wiring for the DIGITAL meter power. Check out the link to the Google page I had included.
BUT, the original poster stated: I recently purchased on EBay a digital display with a 100 Amp shunt...
The wiring on every single Chinese-made DIGITAL ammeter I have seen, and I have seen several, REQUIRED the shunt to be in the negative lead due to the wiring for the DIGITAL meter power. Check out the link to the Google page I had included.
#7
Yes.... I see your point. I have seen these types of meters before and they are trouble. Here's two notes they've posted to the user.
- Common ground design,the ammeter can only series connection between the test equipment negative and the test equipment power supply negative
- Recommend to use a separate isolated power supply