Multiwire Connection - sort of...
Received 0 Votes
I am moving my kitchen from one room to another. I need to move the electrical connections, too. I have a question about a particular outlet box:
If a box has two outlets that are served by two separate 12-2 wires and two separate breakers (not next to each other or bridged), could I connect the two hots separately to the black and red of a 12-3 wire and use those to connect to the two separate outlets in the new location?
So the connection would be:
Wire 1:
Grounds from Wire 1 and Wire 2 tied together with 12-3 Ground and branched in new box for both Outlet Ground connections.
The purpose for these two connections would be to drive the dishwasher and the garbage disposal (both on separate breakers not adjacent to each other).
I hope that is clear enough. Please advise. Thanks!
Wire 1:
12-2 Black => 12-3 Black => Outlet 1 Hot
Wire 2:12-2 Black => 12-3 Red => Outlet 2 Hot
Neutrals from Wire 1 and Wire 2 tied together with 12-3 Neutral and branched in new box for both Outlet Neutral connections.Grounds from Wire 1 and Wire 2 tied together with 12-3 Ground and branched in new box for both Outlet Ground connections.
No..... you want to turn two separate circuits into a multi wire branch circuit.
That you can't do. You would need to extend the two circuits individually.
A multiwire branch circuit requires a common means of disconnect. The code also requires all conductors of a circuit be run together in the same sheath or raceway.
In addition, the neutrals of those two circuits must not be connected together up in the house even where both circuits entered the same outlet box. this is an example of having two wire nutted clusters of neutrals in a box. If a duplex receptacle unit had the top half fed by one of those circuits and the bottom half fed by the other circuit then the bridging tabs between the terminal screws on both sides must be snapped off.
Received 0 Votes
Allanj, would you mind providing more detail on your neutral line management post? I'm curious to learn more. Why wouldn't you tie all the neutrals together? Don't they all go back to the same place?
Parallel current-carrying paths are not allowed for both safety and overload reasons. The safety concern is that you would still have an energized neutral conductor if only one of the breakers was turned off, creating an electrocution hazard for an unwitting serviceman. The overload concern is that if the parallel paths are not constructed nearly identically (which is impossible in a branch circuit), one of the multiple paths will take the bulk of the current. In other words, the current doesn't split equally between parallel paths. If you combined the neutrals of two 20A circuits, one neutral might carry 35A and the other 5A producing an overload condition for #12 wire. The code only allows parallel paths in very specific panel feeder situations, never in branch circuits.
Yeah mossman, the OP question is sort of the opposite of a multiwire (shared neutral) circuit. They are asking about combining neutrals in two or more separate cables. Your understanding of additive current on a properly installed shared neutral circuit is correct.
All the neutrals are tied together at the panel (at the neutral bus bar within) where the breakers for their respective hots are located.
Neutrals for different branch circuits are not tied together in outlet boxes simply because they come togehter in an outlet box they share..
There must be exactly one neutral path from any outlet down to the panel for that branch circuit.
(Ground wires aka equipment grounding conductors from different cables or branch circuits are tied together wherever they come together.)