Iím in the middle of my bathroom Reno and I noticed that the backside of the wall Iíve torn out has furring strips attached to the entire backside of the studs. How does this work with notching and making holes in the studs? Are the furring strips considered part of the entire thickness of the stud?
 
Attached Images  
Sponsored Links
  #2  
Old 01-02-18, 10:15 PM
L
Member
Join Date: Nov 2015
Posts: 1,502
Received 85 Votes on 73 Posts
The code is the hole needs to be 1 1/4" from the edge. As far as I know the furring strips counts as this edge as well.
This is to prevent screw or nail from driven into the wire while installing drywall or other wall finishing material.
 
  #3  
Old 01-03-18, 01:46 AM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Location: USA
Posts: 26,201
Received 714 Votes on 661 Posts
That is national electric code... and is correct, but as far as wall framing codes are concerned, the furring strip is not even there. It is not structural and is not part of the stud.

Wet walls require a 2x6 wall when the size of the hole or notch in either the stud or the plates exceeds code limits.

R602.6... non-load bearing interior walls... holes can be bored up to 60% of stud width, holes no closer than 5/8" to stud edge. Notches not to exceed 40%. Exception: approved stud shoes may be used, following mfg instructions.

Example: https://www.amazon.com/Simpson-Stron.../dp/B001I3OZVI

Up to 2 3/8" o.d.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: