GFCI/AFCI breaker questions


  #1  
Old 02-03-18, 04:14 PM
D
Member
Thread Starter
Join Date: Jun 2017
Posts: 355
Received 0 Upvotes on 0 Posts
Question GFCI/AFCI breaker questions

- Are GFCI or AFCI or combo breakers wider than standard breakers?
- I live in a split level house (3 levels) where potentially my top floor is going to be cutting very close to the 50' limit of the AFCI breaker. Should I install the breaker AND the outlet or just the outlet or just the breaker?
- Are wirenuts inside a breaker box allowed? Are there any special rules?

Thanks!
 
  #2  
Old 02-03-18, 06:35 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
There is no circuit length restrictions on afci breakers. You must be thinking about afci outlets.
I would use afci breaker with gfci outlet. Wire nuts are allowed in the panel.
 
  #3  
Old 02-03-18, 06:46 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
Breaker size varies with brand and version but are usually the same size.
AFCI breaker with GFCI receptacle (assume bathroom) is the norm.
Wirenuts allowed in most areas. I heard some Canadian areas don't like them.

Never heard of a 50' limit. Sorry - 50' limit is for box to 1st AFCI receptacle for 14 gauge wire, 70' for 12 gauge. Don't hear about that very often as most use AFCI breakers.
 
  #4  
Old 02-04-18, 08:20 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,332
Received 877 Upvotes on 740 Posts
- Are GFCI or AFCI or combo breakers wider than standard breakers?
No, but they will be full size breakers (mostly 1") and not thin like you would find in some panels (ex: GE THQP)

cutting very close to the 50' limit of the AFCI breaker. Should I install the breaker AND the outlet or just the outlet or just the breaker?
A AFCI breaker will protect the entire circuit. There is no need for an additional AFCI receptacle (outlet) on the circuit.

- Are wirenuts inside a breaker box allowed? Are there any special rules?
In the USA yes, but it is not allowed in Canada. You just cannot fill the panel over 40% the cross sectional area with conductors or 75% with taps, which is rather difficult to do anyway.
 
 