In the attic I have a splice going to a light I no longer use so I disconnected it. I capped and taped the wires. Is this enough for safety?
Thanks
Thanks
#2
No. Splices must be contained within a junction box.
A small handy box with blank and NM-b romex connector is all you need.
A small handy box with blank and NM-b romex connector is all you need.

#4
Th at will do to. It needs to be fastened to a joist and the cable needs to be stapled within 6" of the box.
#6
Note wire nuts do not need to be taped. There is no reason to cap the ground wire with a wire nut since the whole wire is bare.