Hi all. I've scoured the internet and found some answers to my question...but not to my satisfaction...so I thought I would ask here. I am purchasing a GE slide-in range with an induction cooktop and double oven. This is replacing an older range. I currently have a 50 amp circuit breaker for this device (yes the wire is 6 awg). The manual for the new oven says I should use a 40 amp range cord. It says I can use a 50 amp range cord, but it has to be "marked for use with nominal 1 3/8th diameter connection openings". I don't know what that means exactly? I find this all confusing because there are no 40 amp receptacles. I purchased a new 50 amp receptacle, and feel like I should be able to buy a 50 amp range cord and just call it a day. Or should I use a 40 amp range cord and change my breaker to 40 amp, leaving the 50 amp receptacle in place? Any answers would be highly appreciated, as I want to make sure I do this correctly. It just seems like all the numbers don't match up so it is a bit confusing. Thanks all!
#2
Your search is right in that there is no 40A cord or receptacle. Standard sizes go 15A, 20A, 30A, 50A. The proper size to use for that range is a 50A receptacle and cord set.
Whether you have a three-wire or four-wire circuit will determine if you need the 11-50 configuration or the 14-50 configuration. The manufacturer installation instructions will also have wiring notes for either three-wire or four-wire circuits inside the range wiring compartment.
Whether you have a three-wire or four-wire circuit will determine if you need the 11-50 configuration or the 14-50 configuration. The manufacturer installation instructions will also have wiring notes for either three-wire or four-wire circuits inside the range wiring compartment.
#3
Member
Thread Starter
Join Date: Mar 2018
Location: United States
Posts: 4
Likes: 0
Received 0 Likes
on
0 Posts
Hi Ben...thanks for the quick response. They actually do make 40 amp range cords. They do NOT make 40 amp outlets however. The installation instructions say a 40 amp range cord is required, and that a 50 amp range cord is "not recommended". That's where I am confused. It makes me feel like I should use a 40 amp range cord, and swap out my 50 amp breakers for 40 amp breakers.
#4
Actually.... there are 40A cords available but they fit a 50A receptacle. You can use that cord on a 50A receptacle and change the breaker to a 2P40A.
#5
Member
Thread Starter
Join Date: Mar 2018
Location: United States
Posts: 4
Likes: 0
Received 0 Likes
on
0 Posts
Hey Pete...thanks. I think that's what I'm going to do. I wanted to avoid changing out the breaker but it's an easy (and inexpensive) thing to do so what the heck. I appreciate the feedback and advise!