Wiring a feed grinder


  #1  
Old 04-13-18, 08:57 AM
N
Member
Thread Starter
Join Date: Apr 2018
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wiring a feed grinder

I am planning to wire a new feed grinder. I am wondering about breaker size to power it. Would I need to go to 40 amps twin pole since the start up amps are 31 amps? Here are the specs I have on the machine. Any help would be greatly appreciated. Thank you.
  • 220V
  • 2.0 HP motor
  • 1500 watts
  • Start-up draw 31 amps, under load draw 6-7.5 amps
 
  #2  
Old 04-13-18, 09:04 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Breakers are inherently slow blow devices and since start loads are short there shouldn't be a problem even on a 15 amp circuit..
 

Last edited by ray2047; 04-13-18 at 01:00 PM. Reason: Clarification
  #3  
Old 04-13-18, 12:17 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Either a 15A or 20A double-pole breaker would be OK for this grinder. Virtually all breakers have an HACR rating which means they are designed to allow the start up surge from motors without tripping. Wiring size can be #14 copper if less than 100 feet.
 
 