Some help understanding these wiring diagrams.

Could someone help me decipher these, do the wires go "into" the top or the bottom?

I just need to know how to connect the current to the gfci, the gfci to the breaker and then I suppose by process of elimination I can figure out where the protected circuits come out.

 
  #2  
Old 04-24-18, 04:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Pretty hard to find an answer as all the places that sell those breakers are in Spanish.

I spent 15 minutes searching their site and translating to English. They don't seem to specify line or load.
 
  #3  
Old 04-24-18, 05:39 PM
E
Member
Thread Starter
Join Date: Oct 2014
Posts: 647
Received 5 Upvotes on 5 Posts
Sorry I didn’t mean to make you look so long, I thought maybe the little drawings on the breakers would help.
 
  #4  
Old 04-24-18, 05:59 PM
E
Member
Thread Starter
Join Date: Oct 2014
Posts: 647
Received 5 Upvotes on 5 Posts
are circuit breakers even directional? I remember that with old fashioned fuses it didn't matter which side was which.
 
  #5  
Old 04-24-18, 06:08 PM
L
Member
Join Date: Nov 2015
Posts: 1,573
Received 201 Upvotes on 172 Posts
Breakers themselves are usually non-directional. However, GFCI and AFCI breaker and some breakers with sepecial functions may be directional.

Breakers with screw terminals are usually wired with input on top and load on bottom terminals.
 
  #6  
Old 04-24-18, 06:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Breakers with screw terminals are usually wired with input on top and load on bottom terminals.
Based on one diagram I found..... that is correct. Line in on top. Load on bottom.
 
  #7  
Old 04-24-18, 06:58 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Based on the GFCI breaker diagram I would also agree that line is on top and load on the bottom.

The breaker on the left appears to be a standard breaker and should be able to be wired either way.
 
 