GFCI Outdoor Outlet won't reset


  #1  
Old 05-17-18, 07:43 AM
S
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 18
Received 0 Upvotes on 0 Posts
GFCI Outdoor Outlet won't reset

After a few rainy days, a GFCI outdoor outlet for a pump tripped. Even if I unplug the pump, the GFCI won't reset. I am guessing that it must be a defective GFCI. How can there be a fault without anything plugged into the outlet and no line downstream from this outlet? Would a fault in the line feeding the outlet cause this problem?
I would appreciate any ideas for troubleshooting.
 

Last edited by sssanti; 05-17-18 at 07:48 AM. Reason: typo
  #2  
Old 05-17-18, 09:44 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,095
Received 422 Upvotes on 375 Posts
It's possible the GFI got wet or just failed. Part of the test circuitry is confirming the GFI is working properly. In your case it's not and needs to be replaced.

The other possibility is a loose connection or the breaker actually tripping. Most/all GFIs won't reset if they don't have power. So before you replace, use a multimeter or neon tester to ensure there's voltage coming into the receptacle.
 
  #3  
Old 05-17-18, 10:11 AM
S
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 18
Received 0 Upvotes on 0 Posts
Thanks. I will check if there is power. I also need to double check in case there is anything connected downstream.
 
 