wire in conduit

I am wiring a new garage, I know that I can 9 #12 wires in 1/2 EMT. I want to run 3 separate circuits. Can I run 3 separate hot wires & use a common wire for the ground & neutral branching them off at separate junction boxes?
 
  #2  
Old 08-01-18, 03:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,824
Received 1,330 Votes on 1,229 Posts
Welcome to the forums.

Is this an attached garage ?
 
  #3  
Old 08-01-18, 03:29 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
If using 3 separate single pole breakers for the 3 circuits then each circuit needs it's own neutral. Ground can be shared. One neutral can be shared between 2 hots on opposite legs but the 2 hots must be on a double pole breaker, this is referred to as a multiwire branch circuit.
 
  #4  
Old 08-01-18, 08:01 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,758
Received 97 Votes on 87 Posts
Is this an attached garage ?

Or is this a detached garage? Unless this is an attached garage you cannot run 3 separate circuits to it. You can run one branch circuit or one multiwire branch circuit.
 
 