Is it ok to splice NM and NM-B cable together?

I have the NM 12-2 with ground coming from my breaker. I am installing LED recess lights in my kitchen so I will need to use some new NM-B 12-2 with ground cable for that. If I bring my 12-2 NM cable into a junction box and splice it to my new 12-2 NM-B cable that will be going to my lights is that safe? I know they are rated for different temperatures (60 C and 90 C). I have the kitchen walls down so redoing all the wire back to my splice box will simple enough. I just need to know if that NM to NM-B splice in the junction box will be safe.

Thanks for your time!
 
Attached Images  
  #2  
Old 09-10-18, 06:38 AM
L
Member
Join Date: Nov 2015
Posts: 1,573
Received 201 Upvotes on 172 Posts
That is perfectly safe so long as you don't have a device requiring 90C wire (such as a light fixture) at the splice point.
 
  #3  
Old 09-10-18, 08:37 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
And remember the basics: Junction boxes can not be covered as need to be accessible. Since specifying a metal junction box your ground splice needs to also include the box.
 
  #4  
Old 09-11-18, 05:15 AM
I
Member
Thread Starter
Join Date: Sep 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies. The 3-5 recess lights at the end of the circuit state they need 90 C conductor. That doesn't require 90 C conductor all the way back to the breaker does it?
 
  #5  
Old 09-11-18, 09:52 AM
L
Member
Join Date: Nov 2015
Posts: 1,573
Received 201 Upvotes on 172 Posts
That doesn't require 90 C conductor all the way back to the breaker does it?
No. Just need it where the light fixture is installed.
 
 