20 amp Blank GFI on 15 amp Circuit
We are installing an American Standard 2425 jetted tup and running two 15 amp circuits as per instructions (pump and heater), and running both through GFIs before extending behind the tub to a split outlet. One of the GFI’s will be a plug (a 15amp GFI outlet).
The other I have a BLANK face GFI, but there appears to be NO 15 amp blank face GFI’s made. The one I have is 2 vertical plugs, not a T receptacle(so 15 amp receptacles), but it has 20 amp pass through.
SO…question…because its on a 15amp breaker, it will only pass through 15amps to the end run plug, yes? Otherwise, I am guessing I would have to use another 15amp GFI receptacle? THANKS!
The other I have a BLANK face GFI, but there appears to be NO 15 amp blank face GFI’s made. The one I have is 2 vertical plugs, not a T receptacle(so 15 amp receptacles), but it has 20 amp pass through.
SO…question…because its on a 15amp breaker, it will only pass through 15amps to the end run plug, yes? Otherwise, I am guessing I would have to use another 15amp GFI receptacle? THANKS!
#2
Member
As long as the blank face GFI is rated higher than the breaker (which it is) you're fine. In other words the GFI is rated for 20A, but will never see more than 15A because the main breaker is 15A. DO NOT increase the size of the breaker in the panel.
#3
SO…question…because its on a 15amp breaker, it will only pass through 15amps to the end run plug,
The amount of current is limited by the 15 amp breaker. The dead front GFCI device only provides GFCI protection so I see no problem using a 20 amp dead front device on a 15 amp circuit. I don't remember this question ever coming up in all my years and this is my opinion. I am interested if others have a different opinion.
#6
Member
I doubt 15A dead face GFCI even exists. Even regular duplex GFCI receptacles are actually rated for 20A feed through. Dead face GFCIs are pretty much the same as duplex GFCI receptacles except they don't have slots for a plug.
Regular 15A receptacles are also rated for 20A feed through. Only difference between 15A and 20A is that 20A receptacle allows plugging 20A plug. Internals are practically same.
GFCI does not trip on over current, but at ground fault. Don't see any reason to make 15A model when 20A can cover 15A.
Regular 15A receptacles are also rated for 20A feed through. Only difference between 15A and 20A is that 20A receptacle allows plugging 20A plug. Internals are practically same.
GFCI does not trip on over current, but at ground fault. Don't see any reason to make 15A model when 20A can cover 15A.
#8
Member
Thread Starter
Join Date: Oct 2018
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes this is what was stumping me on this (and of course leave it to me to come up with something "new")! There is surprisingly little info on this scenario, which seems to indicate its not a problem and the 20a blank face is used in this scenario (esp considering they don't make a 15a from everything that I can find).