Running NM cable in furred out residential walls


  #1  
Old 03-05-19, 01:29 PM
J
Member
Thread Starter
Join Date: Mar 2019
Posts: 4
Likes: 0
Received 0 Likes on 0 Posts
Running NM cable in furred out residential walls

I am remodeling my home in Pennsylvania. It is a rowhome, with concrete block party walls. The walls are all open at this point. I will be leaving the original furring strips in place and installing new drywall once the project is complete.

My question is about running NM cable down from the upper floors to the service panel in the basement. I have secured the NM cable to the concrete block every 4 feet vertically. Is this OK? Does the cable have to be metallic, or in a conduit of some sort? It will not be penetrating the block at any point, just straight vertical homeruns.

Thanks in advance.
 
  #2  
Old 03-06-19, 06:33 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Likes: 0
Received 45 Likes on 43 Posts
How deep are the furing strips off the block?
 
  #3  
Old 03-06-19, 06:59 AM
J
Member
Thread Starter
Join Date: Mar 2019
Posts: 4
Likes: 0
Received 0 Likes on 0 Posts
1 by, so 3/4". With 1/2" drywall to hopefully give me the 1-1/4" clearance from nails and whatnot.
 
  #4  
Old 03-06-19, 07:25 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Likes: 0
Received 15 Likes on 13 Posts
How were the electric boxes done before? You really need more than that for most electric boxes. I'd go with 2x2s (actual 1x1). (Guessing a bit. What is so 3/4"?)
 
  #5  
Old 03-06-19, 09:31 AM
J
Member
Thread Starter
Join Date: Mar 2019
Posts: 4
Likes: 0
Received 0 Likes on 0 Posts
The boxes were originally placed in cutouts, where the block was chipped away. I'm not sure how many cubic inches they are, but they're not shallow by any means.
 
  #6  
Old 03-06-19, 03:50 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,401
Received 158 Likes on 139 Posts
Run the cables at least 1 1/4" off to the side of furring strips.
 
  #7  
Old 03-06-19, 04:29 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 15,030
Received 629 Likes on 538 Posts
Add to the furring strips. 3/4" is not enough room for your device boxes. Even handy boxes will be too small.
 
  #8  
Old 03-07-19, 06:31 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,600
Received 156 Likes on 142 Posts
Hi, are the outlet fed now, how was that done?
Geo
 
  #9  
Old 03-07-19, 07:08 AM
J
Member
Thread Starter
Join Date: Mar 2019
Posts: 4
Likes: 0
Received 0 Likes on 0 Posts
The outlets were fed by older NM cable, kind of a silver braided cover. Those old, probably original from the 70s cables, didn't even looked to be secured vertically in the walls. My only concern is if code allows me to secure the NM cable directly to the block, as opposed to needed to go armored or conduit. It won't be exposed anywhere, except possibly at the termination point where they enter the breaker box in the basement.
 
  #10  
Old 03-07-19, 08:30 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,342
Received 462 Likes on 382 Posts
no problem securing to block. The 3/4" gap however is a problem. When going through a stud you require 1-1/4" gap to prevent damage. I'm not sure how that applies to drywall gap between studs.
 
  #11  
Old 03-07-19, 02:03 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,401
Received 158 Likes on 139 Posts
Here are some graphics to help from Mike Holt's site.

https://www.google.com/search?q=mike...C3B1W4RO6YRTM:
 
  #12  
Old 03-07-19, 02:52 PM
M
Member
Join Date: Mar 2009
Location: Northern Virginia
Posts: 4,234
Received 22 Likes on 17 Posts
When going through a stud you require 1-1/4" gap to prevent damage.
Sounds like he won't be running wires through the furring strips.

just straight vertical homeruns
 
  #13  
Old 03-07-19, 03:38 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,342
Received 462 Likes on 382 Posts
Sounds like he won't be running wires through the furring strips.
I realize that, but is the 3/4 gap behind the drywall OK. If the cables were being fished I think it might be OK but the drywall is not up yet so the cables need fastening every 4 feet.
 
  #14  
Old 03-07-19, 05:05 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Likes: 0
Received 15 Likes on 13 Posts
The fact that such small furring strips were used doesn't mean it was the best choice. The wall is open why not do it better.
 
  #15  
Old 03-11-19, 01:53 PM
M
Member
Join Date: Mar 2009
Location: Northern Virginia
Posts: 4,234
Received 22 Likes on 17 Posts
I realize that, but is the 3/4 gap behind the drywall OK. If the cables were being fished I think it might be OK but the drywall is not up yet so the cables need fastening every 4 feet.
I misinterpreted your post. My apologies.
 
 