Ground detected by Extension cord?
#1
Ground detected by Extension cord?
Hi,
Being fairly new to home ownership and eager to fix things at home, I'm encountering the following situation at home:
1. A power strip with ground indicator light is plugged into the wall outlet. The ground indicator light is lighting up green
2. When I opened up the electrical box cover, only a 2 wire cable was run into the box and no ground cable was connected from box to receptacle.
Are the power strip ground tests reliable or am I missing something here?
Thanks
Being fairly new to home ownership and eager to fix things at home, I'm encountering the following situation at home:
1. A power strip with ground indicator light is plugged into the wall outlet. The ground indicator light is lighting up green
2. When I opened up the electrical box cover, only a 2 wire cable was run into the box and no ground cable was connected from box to receptacle.
Are the power strip ground tests reliable or am I missing something here?
Thanks
#2
only a 2 wire cable was run into the box and no ground cable
*Old early versions of NM with ground can be identified by looking for #16 bare wires in the breaker panel.
#3
No it is not reliable. No plug in device that shows a light to indicate a good ground connection is reliable.
Various incorrect and inadequate connections in the home electrical system will also cause the "ground" light to come on. For example if someone tried to use the neutral of a 2 conductor cable to double as the ground connection (not proper) then the ground light will also come on.
Many older systems with metal sheathed flexible conduit will test "correct" for a ground connection but might not have a code compliant, and good and sufficient, ground connection. A 16 gauge ground wire (equipment grounding conductor) in a non-metallic sheathed cable will provide a good ground for some situations but is no longer code compliant. Ten, twelve, and fourteen gauge NM cables e.g. Romex, the most common for household branch circuits, need a built in ground wire of like gauge.
Various incorrect and inadequate connections in the home electrical system will also cause the "ground" light to come on. For example if someone tried to use the neutral of a 2 conductor cable to double as the ground connection (not proper) then the ground light will also come on.
Many older systems with metal sheathed flexible conduit will test "correct" for a ground connection but might not have a code compliant, and good and sufficient, ground connection. A 16 gauge ground wire (equipment grounding conductor) in a non-metallic sheathed cable will provide a good ground for some situations but is no longer code compliant. Ten, twelve, and fourteen gauge NM cables e.g. Romex, the most common for household branch circuits, need a built in ground wire of like gauge.
Last edited by AllanJ; 03-18-19 at 06:52 AM.