Direct Burial cable have to be pvc once in building
#1
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Upgrading to 100 amp service in Garage fed by 200 amp house circuit.I have buried 2 2 2 3 underground 18 inches with pvc 40. I am using direct burial cable.
Once I am in the garage under a roof is pvc required to panel?
Is it required in basement to 200 amp panel?
Can it be run hung correctly without pvc?
Thanks!
KYNETMAN
Once I am in the garage under a roof is pvc required to panel?
Is it required in basement to 200 amp panel?
Can it be run hung correctly without pvc?
Thanks!
KYNETMAN
#2
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,670
Received 259 Upvotes
on
221 Posts
I'm not aware of any direct bury cable that comes in 2-2-2-3. If it is individual conductors without an overall jacket it must be in conduit. Will you please post a picture of the cable or the stamped info written on the cable. If the #2 is aluminum then it's good to 90A. There is direct bury wire that can enter a structure and there is direct bury wire that is not to enter a structure. You need to know which one you have.
Last edited by pattenp; 04-04-19 at 06:08 PM.
#3
Welcome to the forums.
I'm not aware of a 2-2-2-3 underground/direct burial cable either.
How-to-insert-pictures.
I'm not aware of a 2-2-2-3 underground/direct burial cable either.
How-to-insert-pictures.
#5
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,670
Received 259 Upvotes
on
221 Posts
Yes there are 90A breakers. If the 2-2-2-4 is URD it has to be terminated outside the structure. If it's Mobile Home Feeder (MHF) or specifically USE-2/RHH/RHW-2 then it can enter the structure. But either type needs to be in conduit where above ground.