Trying to get constant current from box with 3 way dimmer??
#1
Member
Thread Starter
Trying to get constant current from box with 3 way dimmer??
I am trying to get a constant hotline to some wall sconces that have a separate off on switch at the sconce. The hot line that runs into the box is a 3-way wire and its hooked up to a 3-way dimmer. Is this possible because no matter what I did, as soon as I hit the switch the sconces went out too?
So I have 3 groups of wires coming in the box.
Group 1 is to the can lights
Group 2 is the 3 way with hot
Group 3 is to the wall sconces.
So I have 3 groups of wires coming in the box.
Group 1 is to the can lights
Group 2 is the 3 way with hot
Group 3 is to the wall sconces.
#3
Member
Thread Starter
Its all new wire with neutrals. Wish I could upload a picture but it says I used up my upload space... Any way to delete old uploads?
#5
Member
Thread Starter
Here is a picture. Maybe I can rearrange the wires to get this to work?
Last edited by PJmax; 04-29-19 at 08:53 PM. Reason: imported pic from link
#8
Member
Thread Starter
Thanks for fixing the picture.
Is it because I have the sconce neutral tied in with the 3-way neutral?
Is it because I have the sconce neutral tied in with the 3-way neutral?
#9
You cannot connect the scones there. The three wire cable is two travelers and a neutral. The two wire cable is the can lights. Yes..... you do have neutral there but you only have switched power.
The three way switch at the other end is the hot end.
I also went back and freed up 2mb of storage for you.
The three way switch at the other end is the hot end.
I also went back and freed up 2mb of storage for you.
#10
Member
Thread Starter
Ok, that makes sense. I didn't realize the hot was actually at the other end.
I can just run a separate hot from the box next to it. I may even have enough sconce wire to redirect it into the other box.
Thank you for the help and freeing up some upload space
I can just run a separate hot from the box next to it. I may even have enough sconce wire to redirect it into the other box.
Thank you for the help and freeing up some upload space
#11
Yes. That's why the switches are affecting the power. It either comes in on the black traveler or red traveler depending on the switch position at the other end.
#12
Member
Thread Starter
By code, can I run another wire into this box to grab a hot? It currently has 4 wires going in. I know code only allows a certain amount of wires per cubic inch or something...just not sure exactly
#13
That looks like #14 wiring and it is a two gang deep box. It looks like there is room for an additional two wire cable.