Is there an adapter for me?
I'm new to this forum. Do not know if this question has been answered already. I know almost nothing about electrical technology.
I have a device that was made for me years ago by an electrician in Connecticut , that allowed me to access 2 standard house outlets on different circuits, and then plug a dryer into the device. This gave me the 220 volts I needed for the dryer. The man who made the adapter for me said it was "safe, but not legal".
Now, I live in Alabama. I want to plug this device into 2 circuits so that I can use my toaster oven, microwave and/or coffeemaker at the same time, without overloading a 15-amp circuit.
I'd like to use a 30-amp power strip. Is it possible to purchase an adapter that will plug into my device and allow me to use a power strip that has a standard 3-prong plug?
Is there an adapter made that will work for me?
Is what I'm proposing dangerous?
Is my explanation understandable?
Am I even using the right terminology?
I have a device that was made for me years ago by an electrician in Connecticut , that allowed me to access 2 standard house outlets on different circuits, and then plug a dryer into the device. This gave me the 220 volts I needed for the dryer. The man who made the adapter for me said it was "safe, but not legal".
Now, I live in Alabama. I want to plug this device into 2 circuits so that I can use my toaster oven, microwave and/or coffeemaker at the same time, without overloading a 15-amp circuit.
I'd like to use a 30-amp power strip. Is it possible to purchase an adapter that will plug into my device and allow me to use a power strip that has a standard 3-prong plug?
Is there an adapter made that will work for me?
Is what I'm proposing dangerous?
Is my explanation understandable?
Am I even using the right terminology?
Last edited by Fran S; 07-31-19 at 09:39 PM. Reason: To give locations
#3
Member
No such adapter exists.
This device is dangerous on so many levels and violates so many electrical codes it would take a long time to list them all.
If you own the home you are in now have a line put in for your dryer. If you rent where you are living contact the landlord and request a line be put in.
This device is dangerous on so many levels and violates so many electrical codes it would take a long time to list them all.
If you own the home you are in now have a line put in for your dryer. If you rent where you are living contact the landlord and request a line be put in.
joecaption
voted this post useful.
#4
Forum Topic Moderator
The combining of two 120v circuits into one 240v, like he said, isn't to code, but obviously worked (though of questionable safety).
What you're looking to do to combine two 120v circuits for a 'more powerful' 120v circuit doesn't work. You'll still likely trip your breakers when using multiple appliances at the same time, and cross-connecting circuits can cause other safety issues.
You will have to connect your coffee maker to one circuit, and your toaster to the other. Or make sure you're only using one at a time.
Or the best answer is to have the kitchen upgraded to current code with two 20A circuits at the countertop.
What you're looking to do to combine two 120v circuits for a 'more powerful' 120v circuit doesn't work. You'll still likely trip your breakers when using multiple appliances at the same time, and cross-connecting circuits can cause other safety issues.
You will have to connect your coffee maker to one circuit, and your toaster to the other. Or make sure you're only using one at a time.
Or the best answer is to have the kitchen upgraded to current code with two 20A circuits at the countertop.
#5
Member
Thread Starter
Join Date: Jul 2019
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks
Thanks for your answers. I'm glad I asked before trying this. I don't want anything bad to happen, and now it won't. BTW, I do have a proper dryer hookup where I live now.