Sub panel to shed

I am wanting to install a sub panel (100amp) on the outside of my house. From that panel I want to supply a 12' 24' shed that will be used as a school/playroom (we homeschool) with a small area partitioned off for my workspace. Eventually I may run power (for lights) to a barn from the same sub panel.* Sub panel would be ~65` from the main panel. Main panel is on the back porch. Shed is ~125` from where the sub panel would be and would have another panel to supply lights, 8-10 outlets and a window style AC unit / space heaters.

Run from main to sub panel would be above ground through conduit. Run from sub panel to shed would be underground.*

What size breakers and wires will I need to supply the sub panel?

What size breakers and wires will I need to supply the shed's panel from the sub panel?**
*
 
Sponsored Links
  #2  
Old 08-13-19, 08:48 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,565
Received 249 Votes on 219 Posts
What types of tools/machines would be running in your shop? What size heaters would you be installing?
 
  #3  
Old 08-14-19, 07:48 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,465
Received 102 Votes on 81 Posts
You need to calculate the anticipated loads and also do a voltage drop calculation to determine breaker and wire size.
 
  #4  
Old 08-14-19, 10:13 AM
D
Member
Thread Starter
Join Date: Aug 2019
Posts: 3
Received 0 Votes on 0 Posts
A 20 gallon air compressor and charging for drill batteries will be the main tools used in the workspace with the occasional skill saw/miter saw.
I'll have to figure out what kind of space heater I'll get but it will be a medium sized one from walmart or something similar.
 
  #5  
Old 08-14-19, 11:52 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,465
Received 102 Votes on 81 Posts
This is shooting from the hip without knowing potential amp loads but will most likely fill your needs with no problems. From a 100A breaker in the main panel to the subpanel I'd use 1-1-1-6 in aluminum XHHW-2 conductors if using conduit from panel to panel. For the direct bury run from house subpanel to shed subpanel I'd use 2-2-4-6 Mobile Home Feeder (MHF) and protect it with a 60A breaker in the house subpanel. The shed subpanel can also be a 100A panel and I suggest it to be a main breaker panel. The subpanel at the house only needs to be a main lug panel.
 
  #6  
Old 08-14-19, 04:30 PM
D
Member
Thread Starter
Join Date: Aug 2019
Posts: 3
Received 0 Votes on 0 Posts
Awesome that helps alot! Thank You!!!


 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: