I completed the Tesla Wall charger installation. Thanks for everyone's help on this forum.
Interesting to observe that conduit actually gets warm. 60A circuit breaker even slightly hot when touched on front. Assuming this is expected?
I used 3/4" EMT conduit, 6AWG hots and 8AWG ground. Car can charge max at 48A
Interesting to observe that conduit actually gets warm. 60A circuit breaker even slightly hot when touched on front. Assuming this is expected?
I used 3/4" EMT conduit, 6AWG hots and 8AWG ground. Car can charge max at 48A
#6
Member
Most home breakers have a thermal element that is responsible for small overloads. This will warm the breaker a bit. Also, the wire screws have a torque spec that should be followed. They are to be surprisingly tight.
#7
Member
Thread Starter
I conducted some additional measurements with my IR thermometer.
I was somewhat surprised that there is a significant temperature difference between the two breakers of my 60A breaker assembly.
The one at the bottom gets to about 35C; the one on top 45C. I would expect top to be a bit hotter as heat raises, but 10C ??
I was somewhat surprised that there is a significant temperature difference between the two breakers of my 60A breaker assembly.
The one at the bottom gets to about 35C; the one on top 45C. I would expect top to be a bit hotter as heat raises, but 10C ??
#8
There is a lot of current going through the conductors. It is not surprising that the pipe is getting warm when the charger is at full load.
At 45C the breaker is within the rating of the breaker and terminals. Most newer breakers are rated at 60C or 75C.
At 45C the breaker is within the rating of the breaker and terminals. Most newer breakers are rated at 60C or 75C.
#9
Member
Thread Starter
I guess my surprise is that the one of the breakers of my dual pole gets much warmer than other.
#10
Is the conduit uniformly warm over its entire length or just at the ends?
If one half of the two pole breaker is somewhat warmer than the other, the breaker unit could be worn out or defective, with a loose connection inside. Or somehow the load out of that half of the breaker is greater, which would only occur if there was some 120 volt usage on the branch circuit.
Double check tightness of the terminal screws on the breakers (actually for all breakers and set screws in the panel) But do not use stupendous strength that could strip the screw threads.
If one half of the two pole breaker is somewhat warmer than the other, the breaker unit could be worn out or defective, with a loose connection inside. Or somehow the load out of that half of the breaker is greater, which would only occur if there was some 120 volt usage on the branch circuit.
Double check tightness of the terminal screws on the breakers (actually for all breakers and set screws in the panel) But do not use stupendous strength that could strip the screw threads.
#11
Member
Thread Starter
The conduit is evenly warm over the entire length.
I will double-check the terminal screws.
The breaker is brand new..... (Siemens Siemens Q260)
I will double-check the terminal screws.
The breaker is brand new..... (Siemens Siemens Q260)