Question Red Black and White wires at outlet

EDIT: I figured it out, was written on junction box cover. RED is Hot wired to breaker #3, BLACK is Hot wired to breaker #1... (still no ground wire)
----------------------------------------------------------------------------------------------------------------------------
I had an regular 15 A outlet wired. I had to temporary remove wire from it and unfortunately I didn't take pictures. Now that I"m trying to wire it back I'm confused because junction box has RED, WHITE and BLACK wires. I tested wires and I get 120V between RED and WHITE. But nothing between BLACK and RED or BLACK and WHITE (well I get about 20V there). So black wire is not a ground, but what could it be?
There doesn't seem to be a switch controlling this so I'm confused... I think I'll just wire RED and WHITE to outlet, but I would really like to have ground...
Name:  IMG_3360.JPG
Views: 6167
Size:  2.37 MB
 

Last edited by bratan; 09-12-19 at 09:57 AM.
  #2  
Old 09-12-19, 09:43 AM
B
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 37
Received 0 Upvotes on 0 Posts
I tested between know GROUND and all 3 wires and it appears that RED is HOT and WHITE is neutral. Still not sure what is black for...
 
  #3  
Old 09-12-19, 09:59 AM
B
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 37
Received 0 Upvotes on 0 Posts
Never mind I figured it out There was writing on the junction box cover that I forgot about. It said "#1 is BLACK, #3 is RED". I deciphered that BLACK is HOT connected to breaker #1 in Electric Panel and RED is #3 breaker. Checked and indeed that's the case. Too bad there's still no ground wire
I couldn't get correct multimeter reading because I shut off breaker 1 and 3 at the same time (unintentionally)...
I decided not to remove the post, in case someone has similar issue...
 
  #4  
Old 09-12-19, 10:15 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,894
Received 477 Upvotes on 393 Posts
That is for a split wired receptacle. Cut the tab between the gold screws and connect the black and red wires one each to the gold screws and the white to one of the silver screws. This gives the ability to use two high current devices without tripping a breaker. Each socket can supply up to 15 amps.
 
bratan voted this post useful.
  #5  
Old 09-12-19, 10:28 AM
B
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 37
Received 0 Upvotes on 0 Posts
Thanks Joed! That makes total sense. I guess this can take double the load (i.e. 30 AMP)?
 
  #6  
Old 09-12-19, 12:03 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes on 204 Posts
No it doesn't double the load to 30A. You have two separate circuits on two different 15A breakers, so the load on each circuit can still only be 15A. The circuits are 180deg out of phase to each other so the neutral will only ever be maxed at 15A. In other words the neutral will only be carrying the imbalanced amperage between the two circuits.
 
  #7  
Old 09-12-19, 12:41 PM
B
Member
Thread Starter
Join Date: Dec 2009
Location: USA
Posts: 37
Received 0 Upvotes on 0 Posts
Not sure I understand. Can I plug in two device, each 15 AMP into each socket of the outlet?
 
  #8  
Old 09-12-19, 01:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,040
Received 3,416 Upvotes on 3,063 Posts
Yes.... that duplex receptacle will now deliver 30A of 120v power. 15A on each side of the receptacle.

That looks like older style BX cable which to a certain extent is your ground.
Make sure the clamp holding it to the box is tight.
 
bratan voted this post useful.
 