Dock lighting needs GFCI?
I'm working still on a dock design. Seems there is NEC rqmts about lighting circuits near pools and in crawlspaces needing GFCI, but anything about a dock siting right over salt water?
#3
Looking in Art 682 (Natural and Artificially made bodies of water), I do not see anything about GFCI protection for lighting. All receptacles, of course, do require GFCI protection.
@ Luke, Why not low voltage AC? It would have the same shock hazard. (none)
@ Luke, Why not low voltage AC? It would have the same shock hazard. (none)
#5
Thinking of LED with dimmable drivers, like the Ikea stuff. The damp rating demand is a bit of a problem. May have to deal with yet more 3R or 4X boxes. Will tie in to the wireless remote boat lift controls.
Tony: i think dedicated use recepts, like a 30 amp twist lock does not need gfci?? But right alongside, i have a 240v hardwired lift system that does need gfci.
Tony: i think dedicated use recepts, like a 30 amp twist lock does not need gfci?? But right alongside, i have a 240v hardwired lift system that does need gfci.
#6
i think dedicated use recepts, like a 30 amp twist lock does not need gfci??
#7
Tony; do you have access to that text about 100A?
All I have access to is this, from the NEC summary page:
GFCI protection is required by the 2017 NEC for newly installed and replacement 15 and 20 amp receptacles on kitchen countertops, in bathrooms, outdoor areas, unfinished basements and crawl spaces, garages, boathouses, laundry areas, and within 6’ of sinks, bathtubs and shower stalls. GFCI protection is also required for certain appliances that have a history of being a shock hazard. Drinking fountains, vending machines, dishwashers and boat hoists are examples of appliances that require GFCI protection.
I know there has been a lot of pushback to the marinas using 30mA protected service to commercial boat docks feeding both 30A and 50A services, via twist locks.
Here is a good read on the 30mA rule with 2017 code.
https://www.marinadockage.com/techni...s-marina-code/
All I have access to is this, from the NEC summary page:
GFCI protection is required by the 2017 NEC for newly installed and replacement 15 and 20 amp receptacles on kitchen countertops, in bathrooms, outdoor areas, unfinished basements and crawl spaces, garages, boathouses, laundry areas, and within 6’ of sinks, bathtubs and shower stalls. GFCI protection is also required for certain appliances that have a history of being a shock hazard. Drinking fountains, vending machines, dishwashers and boat hoists are examples of appliances that require GFCI protection.
I know there has been a lot of pushback to the marinas using 30mA protected service to commercial boat docks feeding both 30A and 50A services, via twist locks.
Here is a good read on the 30mA rule with 2017 code.
https://www.marinadockage.com/techni...s-marina-code/
Last edited by telecom guy; 10-27-19 at 06:40 AM.
#8
do you have access to that text about 100A?