RV Electrical Panel


  #1  
Old 11-25-19, 03:32 AM
S
Member
Thread Starter
Join Date: Apr 2019
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Smile RV Electrical Panel

Im running an rv panel 300ft with a 30 amp and 50 amp plugs. The 30 amp will be for an rv and the 50 amp will be for a 40 amp electric car charger. Wondering if #2 aluminum wire would be big enough to carry this also what size breaker to use? And do I need a grounding rod at the rv panel?
 
  #2  
Old 11-25-19, 09:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,741 Upvotes on 3,356 Posts
#2 aluminum i good for at least 90A. 90A-100A breaker.
Your RV panel is considered a sub panel so you will need four wires. Two hots, neutral and ground.
The neutral and ground must remain separate.
Yes.... you will need a ground rod there connected to the ground wire only.
 
  #3  
Old 11-25-19, 10:12 AM
S
Member
Thread Starter
Join Date: Apr 2019
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
I already new needing 4 wires, just wondering on size......Thanks
 
 