Confused about electrical wiring
I have an outlet where the neutral is acting as ground. And ground is the neutral.. just bought the house. I've opened all outlets and lights and i can't see anything crossed anywhere,, there's no junction boxes in the attic,, what do i do??
#2
In a properly constructed and properly wired system you will always measure about 120 volts hot to neutal, about 120 volts hot to ground, and about 0 volts neutral to ground at receptacles.
This is true when ground and neutral are properly interconnected (bonded) at the panel where the first whole-house disconnect is located.
.
This is true when ground and neutral are properly interconnected (bonded) at the panel where the first whole-house disconnect is located.
.